[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] Sharp Increase on Air Temperature when Heating is initially on?





You could:

1) reduce the capacity of the system (I don't know how you sized it)
2) increase the zone interior thermal mass

Example:

InternalMass,
  Basement Internal Mass,  !- Name
  InteriorFurnishings,  !- Construction Name
  Basement,  !- Zone Name
  7126.2120;  !- Surface Area

Construction,
    InteriorFurnishings,     !- Name
    Std Wood 6inch;          !- Outside Layer

by changing thickness or density

Material,
    Std Wood 6inch,          !- Name
    MediumSmooth,            !- Roughness
    0.15,                    !- Thickness {m}
    0.12,                    !- Conductivity {W/m-K}
##if #[Construction_Type[] EQS Heavy]
   1080.0000,                !- Density {kg/m3}
##elseif #[Construction_Type[] EQS Light]
    540.0000,                !- Density {kg/m3}
##endif
    1210,                    !- Specific Heat {J/kg-K}
    0.9000000,               !- Thermal Absorptance
    0.7000000,               !- Solar Absorptance
    0.7000000;               !- Visible Absorptance

3) tweak the air thermal capacitance - ZoneCapacitanceMultiplier:ResearchSpecial

On 7/14/2011 6:16 AM, Denis wrote:
 

Hi everyone,

I am new to E+, and hope if some of you can help me out on this.

I have a simple system, district heating as the supply heat source, which then connected to a radiator (currently using Baseboard:Convective:Water object) for the demand side. A constant flow rate pump is on the inlet side of the supply part, and the remaining node connections are in Pipe:Adiabatic.

The building is a single zone, one story house, with a setpoint schedule for the room thermostat as:

00:00 - 07:00: 10 deg C
07:00 - 23:00: 21 deg C
23:00 - 24:00: 10 deg C

Since the Air Temperature is well above the setpoint between 00:00 - 07:00, and so the heating wouldn't kicked in after 07:00. What I am not so sure about is the rate of temperature increase is too quick (about 2 deg C per 10 minutes). I have tried adding some air infiltration, but occasionally the HVAC system doesn't converge at its maximum iterations. Is there any other heat source component that I can use, which can simulated a more graduated increase in the air temperature?

Many thanks,
Denis



-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years


__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___