[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

[EnergyPlus_Support] Re: Sharp Increase on Air Temperature when Heating is initially on?



Thanks Richard,

Increase the air thermal capacitance at the ZoneCapacitanceMultiplier:ResearchSpecial object does help delaying the sharp increase on Air Temperature.

I set the capacity of the system, and the district heating's nominal capacity to be 6kW, one warning I am having all the time is:

** Warning ** No valid range found for Loop Demand=14990.27 in Load Range Based Operation Scheme=HW HEATING OPERATION.
**   ~~~   ** All equipment will be turned off. Other cases of this condition will not be reported.
**   ~~~   **  During Warmup ... ...

of which HW HEATING OPERATION has an upper limit of 6kW. I checked the result and couldn't find any load demand that is higher than 6kW. In this case, can I ignore this warning, or I need to be careful regarding to why this has happened?

Many thanks,
Denis

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Richard Raustad <RRaustad@...> wrote:
>
> You could:
> 
> 1) reduce the capacity of the system (I don't know how you sized it)
> 2) increase the zone interior thermal mass
> 
> Example:
> 
> InternalMass,
>    Basement Internal Mass,  !- Name
>    InteriorFurnishings,  !- Construction Name
>    Basement,  !- Zone Name
>    7126.2120;  !- Surface Area
> 
> Construction,
>      InteriorFurnishings,     !- Name
>      Std Wood 6inch;          !- Outside Layer
> 
> by changing thickness or density
> 
> Material,
>      Std Wood 6inch,          !- Name
>      MediumSmooth,            !- Roughness
>      0.15,                    !- Thickness {m}
>      0.12,                    !- Conductivity {W/m-K}
> ##if #[Construction_Type[] EQS Heavy]
>     1080.0000,                !- Density {kg/m3}
> ##elseif #[Construction_Type[] EQS Light]
>      540.0000,                !- Density {kg/m3}
> ##endif
>      1210,                    !- Specific Heat {J/kg-K}
>      0.9000000,               !- Thermal Absorptance
>      0.7000000,               !- Solar Absorptance
>      0.7000000;               !- Visible Absorptance
> 
> 3) tweak the air thermal capacitance - 
> ZoneCapacitanceMultiplier:ResearchSpecial
> 
> On 7/14/2011 6:16 AM, Denis wrote:
> >
> > Hi everyone,
> >
> > I am new to E+, and hope if some of you can help me out on this.
> >
> > I have a simple system, district heating as the supply heat source, 
> > which then connected to a radiator (currently using 
> > Baseboard:Convective:Water object) for the demand side. A constant 
> > flow rate pump is on the inlet side of the supply part, and the 
> > remaining node connections are in Pipe:Adiabatic.
> >
> > The building is a single zone, one story house, with a setpoint 
> > schedule for the room thermostat as:
> >
> > 00:00 - 07:00: 10 deg C
> > 07:00 - 23:00: 21 deg C
> > 23:00 - 24:00: 10 deg C
> >
> > Since the Air Temperature is well above the setpoint between 00:00 - 
> > 07:00, and so the heating wouldn't kicked in after 07:00. What I am 
> > not so sure about is the rate of temperature increase is too quick 
> > (about 2 deg C per 10 minutes). I have tried adding some air 
> > infiltration, but occasionally the HVAC system doesn't converge at its 
> > maximum iterations. Is there any other heat source component that I 
> > can use, which can simulated a more graduated increase in the air 
> > temperature?
> >
> > Many thanks,
> > Denis
> >
> >
> > 
> 
> -- 
> Richard A. Raustad
> Senior Research Engineer
> Florida Solar Energy Center
> University of Central Florida
> 1679 Clearlake Road
> Cocoa, FL  32922-5703
> Phone:   (321) 638-1454
> Fax:     (321) 638-1439 or 1010
> Visit our web site at: http://www.fsec.ucf.edu
> 
> UCF - From Promise to Prominence: Celebrating 40 Years
>




------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/