[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

[EnergyPlus_Support] Re: Problem with removing reheat coils in VAV



Post some code snipbits, like the setpoint manager.

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "n_junk" <n_junk@...> wrote:
>
> Many thanks for your help, but I still have the same problem.
> 
> I changed the scheduled setpointmanager for the singlezone:heating, but it made no difference.
> 
> What I did was this: 
> - opened the example file "HVACTemplate-5ZonePackagedVAV.idf" with the Chicago weather file;
> - changed the thermostat so that the interior temperature should be between 20-25ºC (with the reheat coils active the temperature stays in this limit, so the problem is not from here);
> - removed the reheat coils and the cooling coil;
> - removed all the lights and electric equipment and most of the people (just to eliminate the influence of internal heating loads);
> - changed the heating design temperature from 10ºC to 40ºC;
> - deleted the SetpointManager:Scheduled for Heating and created the SetpointManager:SingleZone:Heating, using the Space3-1 as the control zone name (it's the zone with more heating demands).
> 
> And then the temperatures of Space3-1 (and others) are not hot enough. What else can be wrong? Could the problem be in the setpointmanager: MixedAir ?
> 
> Thanks in advance!
> 
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Richard Raustad <RRaustad@> wrote:
> >
> > If you remove the terminal unit heating coils, you can no longer control 
> > the air loop heating coil at a constant supply air temperature (i.e., 
> > using a scheduled temperature set point). Verify how the main heating 
> > coil is controlled (i'm guessing scheduled) and use a different type of 
> > set point manager to control it (e.g., SetpointManager:SingleZone:Heating).
> > 
> > On 7/11/2011 7:01 PM, n_junk wrote:
> > >
> > >
> > > Hi! You are refering to "Central Heating Design Supply Air 
> > > Temperature", right? I forgot to tell that I already had changed it to 
> > > 20, 30, 40, 50 and even 70ºC and none of them hadn't change at all the 
> > > interior temperature. If I use a high temperature and put again the 
> > > reheat coils, the rooms sometimes even overheat, but without them the 
> > > temperatures continues under 20ºC.
> > >
> > > This is really odd, I don't know what is happening.
> > >
> > > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx 
> > > <mailto:EnergyPlus_Support%40yahoogroups.com>, Vinay Devanathan 
> > > <vinay.devanathan@> wrote:
> > > >
> > > > The main heating coils setpoint temperature will be set such that it 
> > > only
> > > > heats air to a certain temp, (say around 15 - 16 C), so that the reheat
> > > > coils can be sized for proper capacity to meet the load. When you 
> > > remove the
> > > > reheat coils, your supply air will obviously be under-heated as the main
> > > > heating coil is not sized for that high capacity and will end up 
> > > providing
> > > > supply air at the setpoint temperature. You can look at what the heating
> > > > coils design leaving air temperature by viewing the expidf file under
> > > > Sizing:System object.
> > > >
> > > > On Mon, Jul 11, 2011 at 1:02 PM, n_junk@ <
> > > > n_junk@> wrote:
> > > >
> > > > > **
> > > > >
> > > > >
> > > > > Hi!
> > > > >
> > > > > I'm trying to simulate an existing HVAC system which is similar to 
> > > a VAV,
> > > > > only with heating, without cooling coil or reheat coils. I'm using 
> > > the HVAC
> > > > > Template VAV Packaged.
> > > > > The rooms' temperatures stay above 20ºC, like I configured in the
> > > > > Thermostat, until I remove the reheat coils. When I do that the 
> > > temperature
> > > > > drops under 20ºC and only reaches it if there are internal loads.
> > > > >
> > > > > I have almost everything in autosize, except the maximum flow of 
> > > the input
> > > > > air (but autosize never reaches it, so I think the problem is not from
> > > > > there).
> > > > >
> > > > > To see my problem just open this example file that comes with 
> > > EnergyPlus:
> > > > > HVACTemplate-5ZonePackagedVAV.idf. Then run a simulation and 
> > > consult the
> > > > > evolution of Zone Air Temperature for any of the conditioned zones 
> > > and see
> > > > > that it stays inside the temperatures of the Thermostat. After 
> > > that go to
> > > > > the file, remove the reheat coils of every zone (and deactivate 
> > > the system
> > > > > cooling coil), run the simulation again and compare the 
> > > temperatures. You'll
> > > > > see that now the temperatures stay under the Thermostat limit and 
> > > only reach
> > > > > it when the internal loads harm the room enough.
> > > > >
> > > > > I'm looking in the expidf file for days and I still don't know what is
> > > > > wrong with it. Since I really have to remove the reheat coils, 
> > > what can I do
> > > > > to correct this problem?
> > > > >
> > > > > Thanks in advance!
> > > > >
> > > > >
> > > > >
> > > >
> > >
> > > 
> > 
> > -- 
> > Richard A. Raustad
> > Senior Research Engineer
> > Florida Solar Energy Center
> > University of Central Florida
> > 1679 Clearlake Road
> > Cocoa, FL  32922-5703
> > Phone:   (321) 638-1454
> > Fax:     (321) 638-1439 or 1010
> > Visit our web site at: http://www.fsec.ucf.edu
> > 
> > UCF - From Promise to Prominence: Celebrating 40 Years
> >
>




------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/