got the file...
fist impressions:
combining a unitary unit with an extra coil is always troublesome.
there is an "in-built" setpoint manager in the unitary unit which you can't get to. this unit will put set-points on nodes to try and do it's thing even if the coil or unit is OFF for all days.
The only setpoint manager + controller that you have is on your ODA Mixer. I would create an extra controller and mixer for the heating coil.
I got a system to work with a unitary:heatcool where i turned off the gas heating coil, and inserted a water heating coil after the system...but it gave me many a hassel. see excerpt below:
!JMM VENTILATION 118129
Sizing:System,
118129 AHU, !- AirLoop Name
Sensible, !- Type of Load to Size On
0.016944, !- Design Outdoor Air Flow Rate {m3/s}
1, !- Minimum System Air Flow Ratio
7, !- Preheat Design Temperature {C}
0.008, !- Preheat Design Humidity Ratio {kg-H2O/kg-Air}
11, !- Precool Design Temperature {C}
0.008, !- Precool Design Humidity Ratio {kg-H2O/kg-Air}
14, !- Central Cooling Design Supply Air Temperature {C}
34, !- Central Heating Design Supply Air Temperature {C}
NonCoincident, !- Sizing Option
No, !- 100% Outdoor Air in Cooling
No, !- 100% Outdoor Air in Heating
0.008, !- Central Cooling Design Supply Air Humidity Ratio {kg-H2O/kg-Air}
0.008, !- Central Heating Design Supply Air Humidity Ratio {kg-H2O/kg-Air}
DesignDay, !- Cooling Design Air Flow Method
0, !- Cooling Design Air Flow Rate {m3/s}
DesignDay, !- Heating Design Air Flow Method
0; !- Heating Design Air Flow Rate {m3/s}
AirLoopHVAC,
118129 AHU, !- Name
, !- Controller List Name
118129 AHU Availability Managers, !- Availability Manager List Name
autosize, !- Design Supply Air Flow Rate {m3/s}
118129 AHU Branches, !- Branch List Name
, !- Connector List Name
118129 AHU Air Loop Inlet, !- Supply Side Inlet Node Name
118129 AHU Return Air Outlet, !- Demand Side Outlet Node Name
118129 AHU Supply Path Inlet, !- Demand Side Inlet Node Names
118129 AHU Air Loop Outlet; !- Supply Side Outlet Node Names
BranchList,
118129 AHU Branches, !- Name
118129 AHU Main Branch; !- Branch 1 Name
Branch,
118129 AHU Main Branch, !- Name
autosize, !- Maximum Flow Rate {m3/s}
, !- Pressure Drop Curve Name
AirLoopHVAC:OutdoorAirSystem, !- Component 1 Object Type
118129 AHU OA System, !- Component 1 Name
118129 AHU Air Loop Inlet, !- Component 1 Inlet Node Name
118129 AHU Mixed Air Outlet, !- Component 1 Outlet Node Name
Passive, !- Component 1 Branch Control Type
AirLoopHVAC:Unitary:Furnace:HeatCool, !- Component 2 Object Type
118129 AHU Furnace with DX Cooling, !- Component 2 Name
118129 AHU Mixed Air Outlet, !- Component 2 Inlet Node Name
118129 Unitary Unit Outlet, !- Component 2 Outlet Node Name
Passive, !- Component 2 Branch Control Type
Coil:Heating:Water, !- Component 3 Object Type
118129 AHU Heating Coil, !- Component 3 Name
118129 Unitary Unit Outlet, !- Component 3 Inlet Node Name
118129 AHU Air Loop Outlet, !- Component 3 Outlet Node Name
Active; !- Component 3 Branch Control Type
AirLoopHVAC:SupplyPath,
118129 AHU Supply Path, !- Name
118129 AHU Supply Path Inlet, !- Supply Air Path Inlet Node Name
AirLoopHVAC:ZoneSplitter,!- Component 1 Object Type
118129 AHUAirLoopHVAC:ZoneSplitter; !- Component 1 Name
AirLoopHVAC:ZoneSplitter,
118129 AHUAirLoopHVAC:ZoneSplitter, !- Name
118129 AHU Supply Path Inlet, !- Inlet Node Name
118129 Zone Equip Inlet; !- Outlet 1 Node Name
AirLoopHVAC:ReturnPath,
118129 AHU Return Path, !- Name
118129 AHU Return Air Outlet, !- Return Air Path Outlet Node Name
AirLoopHVAC:ZoneMixer, !- Component 1 Object Type
118129 AHUAirLoopHVAC:ZoneMixer; !- Component 1 Name
AirLoopHVAC:ZoneMixer,
118129 AHUAirLoopHVAC:ZoneMixer, !- Name
118129 AHU Return Air Outlet, !- Outlet Node Name
118129 Return Outlet; !- Inlet 1 Node Name
AvailabilityManagerAssignmentList,
118129 AHU Availability Managers, !- Name
AvailabilityManager:NightCycle, !- Availability Manager 1 Object Type
118129 AHU Availability; !- Availability Manager 1 Name
AvailabilityManager:NightCycle,
118129 AHU Availability, !- Name
HVACTemplate-Always 1, !- Applicability Schedule Name
12345, !- Fan Schedule Name
CycleOnAny, !- Control Type
8, !- Thermostat Tolerance {deltaC}
300, !- Cycling Run Time {s}
118129; !- Control Zone Name
AirLoopHVAC:Unitary:Furnace:HeatCool,
118129 AHU Furnace with DX Cooling, !- Name
HVACTemplate-Always 1, !- Availability Schedule Name
118129 AHU Mixed Air Outlet, !- Furnace Air Inlet Node Name
118129 Unitary Unit Outlet, !- Furnace Air Outlet Node Name
HVACTemplate-Always 1, !- Supply Air Fan Operating Mode Schedule Name
80, !- Maximum Supply Air Temperature {C}
autosize, !- Supply Air Flow Rate During Cooling Operation {m3/s}
autosize, !- Supply Air Flow Rate During Heating Operation {m3/s}
autosize, !- Supply Air Flow Rate When No Cooling or Heating is Needed {m3/s}
118129, !- Controlling Zone or Thermostat Location
Fan:ConstantVolume, !- Supply Fan Object Type
118129 AHU Supply Fan, !- Supply Fan Name
BlowThrough, !- Fan Placement
Coil:Heating:Gas, !- Heating Coil Object Type
118129 AHU Heating Coil Gas, !- Heating Coil Name
Coil:Cooling:DX:SingleSpeed, !- Cooling Coil Object Type
118129 AHU Cooling Coil, !- Cooling Coil Name
None, !- Dehumidification Control Type
, !- Reheat Coil Object Type
; !- Reheat Coil Name
!using the enclosed motor at 1800 rpm ASHRAE 90.1-2007 Table 10.8 (%)
Fan:ConstantVolume,
118129 AHU Supply Fan, !- Name
12345, !- Availability Schedule Name
0.7, !- Fan Efficiency
1781.818182, !- Pressure Rise {Pa}
autosize, !- Maximum Flow Rate {m3/s}
0.825, !- Motor Efficiency
0, !- Motor In Airstream Fraction
118129 AHU Mixed Air Outlet, !- Air Inlet Node Name
118129 AHU Supply Fan Outlet; !- Air Outlet Node Name
Coil:Heating:Gas,
118129 AHU Heating Coil Gas, !- Name
HVACTemplate-Always 0, !- Availability Schedule Name
0.8, !- Gas Burner Efficiency
0, !- Nominal Capacity {W}
118129 AHU Supply Fan Outlet, !- Air Inlet Node Name
118129 AHU Gas Heating Coil Outlet, !- Air Outlet Node Name
, !- Temperature Setpoint Node Name
!118129 Zone Equip Inlet, !- Temperature Setpoint Node Name
0, !- Parasitic Electric Load {W}
118129 AHU Heating Coil PLF-FPLR, !- Part Load Fraction Correlation Curve Name
0; !- Parasitic Gas Load {W}
Curve:Cubic,
118129 AHU Heating Coil PLF-FPLR, !- Name
0.8, !- Coefficient1 Constant
0.2, !- Coefficient2 x
0, !- Coefficient3 x**2
0, !- Coefficient4 x**3
0, !- Minimum Value of x
1; !- Maximum Value of x
Coil:Cooling:DX:SingleSpeed,
118129 AHU Cooling Coil, !- Name
HVACTemplate-Always 1, !- Availability Schedule Name
autosize, !- Rated Total Cooling Capacity {W}
autosize, !- Rated Sensible Heat Ratio
3.81, !- Rated COP
autosize, !- Rated Air Flow Rate {m3/s}
, !- Rated Evaporator Fan Power Per Volume Flow Rate {W/(m3/s)}
118129 AHU Gas Heating Coil Outlet, !- Air Inlet Node Name
118129 Unitary Unit Outlet, !- Air Outlet Node Name
118129 AHU DX Coil Cap-FT, !- Total Cooling Capacity Function of Temperature Curve Name
118129 AHU DX Coil Cap-FF, !- Total Cooling Capacity Function of Flow Fraction Curve Name
118129 AHU DX Coil EIR-FT, !- Energy Input Ratio Function of Temperature Curve Name
118129 AHU DX Coil EIR-FF, !- Energy Input Ratio Function of Flow Fraction Curve Name
118129 AHU DX Coil PLF, !- Part Load Fraction Correlation Curve Name
0, !- Nominal Time for Condensate Removal to Begin {s}
0, !- Ratio of Initial Moisture Evaporation Rate and Steady State Latent Capacity {dimensionless}
0, !- Maximum Cycling Rate {cycles/hr}
0, !- Latent Capacity Time Constant {s}
118129 AHU Cooling Coil Condenser Inlet, !- Condenser Air Inlet Node Name
AirCooled, !- Condenser Type
0, !- Evaporative Condenser Effectiveness {dimensionless}
, !- Evaporative Condenser Air Flow Rate {m3/s}
0, !- Evaporative Condenser Pump Rated Power Consumption {W}
0, !- Crankcase Heater Capacity {W}
10; !- Maximum Outdoor Dry-Bulb Temperature for Crankcase Heater Operation {C}
! DOE-2.1E, COOL-CAP-FT for PTAC w/ SI temps
Curve:Biquadratic,
118129 AHU DX Coil Cap-FT, !- Name
0.942587793, !- Coefficient1 Constant
0.009543347, !- Coefficient2 x
0.00068377, !- Coefficient3 x**2
-0.011042676, !- Coefficient4 y
0.000005249, !- Coefficient5 y**2
-0.00000972, !- Coefficient6 x*y
12.77778, !- Minimum Value of x
23.88889, !- Maximum Value of x
18.0, !- Minimum Value of y
46.11111; !- Maximum Value of y
! DOE-2.1E, RATED-CCAP-FFLOW for PTAC
Curve:Quadratic,
118129 AHU DX Coil Cap-FF, !- Name
0.8, !- Coefficient1 Constant
0.2, !- Coefficient2 x
0, !- Coefficient3 x**2
0.5, !- Minimum Value of x
1.5; !- Maximum Value of x
! DOE-2.1E, COOL-EIR-FT for PTAC w/ SI temps
Curve:Biquadratic,
118129 AHU DX Coil EIR-FT, !- Name
0.342414409, !- Coefficient1 Constant
0.034885008, !- Coefficient2 x
-0.0006237, !- Coefficient3 x**2
0.004977216, !- Coefficient4 y
0.000437951, !- Coefficient5 y**2
-0.000728028, !- Coefficient6 x*y
12.77778, !- Minimum Value of x
23.88889, !- Maximum Value of x
18.0, !- Minimum Value of y
46.11111; !- Maximum Value of y
! DOE-2.1E, RATED-CEIR-FFLOW for PTAC
Curve:Quadratic,
118129 AHU DX Coil EIR-FF, !- Name
1.1552, !- Coefficient1 Constant
-0.1808, !- Coefficient2 x
0.0256, !- Coefficient3 x**2
0.5, !- Minimum Value of x
1.5; !- Maximum Value of x
! PLF = l.- Cd(1.-PLR) where Cd = 0.15
Curve:Quadratic,
118129 AHU DX Coil PLF, !- Name
0.85, !- Coefficient1 Constant
0.15, !- Coefficient2 x
0, !- Coefficient3 x**2
0, !- Minimum Value of x
1; !- Maximum Value of x
OutdoorAir:Node,
118129 AHU Cooling Coil Condenser Inlet, !- Name
-1; !- Height Above Ground {m}
Coil:Heating:Water,
118129 AHU Heating Coil, !- Name
HVACTemplate-Always 1, !- Availability Schedule Name
, !- U-Factor Times Area Value {W/K}
, !- Maximum Water Flow Rate {m3/s}
118129 AHU Heating Coil HW Inlet, !- Water Inlet Node Name
118129 AHU Heating Coil HW Outlet, !- Water Outlet Node Name
118129 Unitary Unit Outlet, !- Air Inlet Node Name
118129 AHU Air Loop Outlet, !- Air Outlet Node Name
, !- Performance Input Method
autosize, !- Rated Capacity {W}
, !- Rated Inlet Water Temperature {C}
, !- Rated Inlet Air Temperature {C}
, !- Rated Outlet Water Temperature {C}
; !- Rated Outlet Air Temperature {C}
!N4 , \field Rated Inlet Water Temperature
!\units C
!\type real
!\default 82.2
!N5, \field Rated Inlet Air Temperature
!\units C
!\type real
!\default 16.6
!N6, \field Rated Outlet Water Temperature
!\units C
!\type real
!\default 71.1
!N7; \field Rated Outlet Air Temperature
!\units C
!\type real
!\default 32.2
Branch,
118129 AHU HW Branch, !- Name
, !- Maximum Flow Rate {m3/s}
, !- Pressure Drop Curve Name
Coil:Heating:Water, !- Component 1 Object Type
118129 AHU Heating Coil, !- Component 1 Name
118129 AHU Heating Coil HW Inlet, !- Component 1 Inlet Node Name
118129 AHU Heating Coil HW Outlet, !- Component 1 Outlet Node Name
Active; !- Component 1 Branch Control Type
Controller:WaterCoil,
118129 AHU HW Branch Controller, !- Name
Temperature, !- Control Variable
Normal, !- Action
Flow, !- Actuator Variable
118129 Zone Air Node, !- Sensor Node Name !118129 Zone Air Node
118129 AHU Heating Coil HW Inlet, !- Actuator Node Name
autosize, !- Controller Convergence Tolerance {deltaC}
autosize, !- Maximum Actuated Flow {m3/s}
0.0; !- Minimum Actuated Flow {m3/s}
OutdoorAir:NodeList,
118129 AHU Outside Air Inlet; !- Node or NodeList Name 1
AirLoopHVAC:OutdoorAirSystem,
118129 AHU OA System, !- Name
118129 AHU OA System Controllers, !- Controller List Name
118129 AHU OA System Equipment, !- Outdoor Air Equipment List Name
118129 AHU Availability Managers; !- Availability Manager List Name
AirLoopHVAC:ControllerList,
118129 AHU OA System Controllers, !- Name
Controller:OutdoorAir, !- Controller 1 Object Type
118129 AHU OA Controller,!- Controller 1 Name
Controller:WaterCoil,!- Controller 2 Object Type
118129 AHU HW Branch Controller; !- Controller 2 Name
AirLoopHVAC:OutdoorAirSystem:EquipmentList,
118129 AHU OA System Equipment, !- Name
OutdoorAir:Mixer, !- Component 1 Object Type
118129 AHU OA Mixing Box;!- Component 1 Name
OutdoorAir:Mixer,
118129 AHU OA Mixing Box,!- Name
118129 AHU Mixed Air Outlet, !- Mixed Air Node Name
118129 AHU Outside Air Inlet, !- Outdoor Air Stream Node Name
118129 AHU Relief Air Outlet, !- Relief Air Stream Node Name
118129 AHU Air Loop Inlet; !- Return Air Stream Node Name
SetpointManager:SingleZone:Heating,
118129 Heating Supply Air Temp Manager, !- Name
Temperature, !- Control Variable
-99., !- Minimum Supply Air Temperature {C}
34., !- Maximum Supply Air Temperature {C}
118129, !- Control Zone Name
118129 Zone Air Node, !- Zone Node Name
118129 Zone Equip Inlet, !- Zone Inlet Node Name
118129 AHU Air Loop Outlet; !- Setpoint Node or NodeList Name
SetpointManager:SingleZone:Cooling,
118129 Heating Supply Air Temp Manager, !- Name
Temperature, !- Control Variable
-99., !- Minimum Supply Air Temperature {C}
34., !- Maximum Supply Air Temperature {C}
118129, !- Control Zone Name
118129 Zone Air Node, !- Zone Node Name
118129 Zone Equip Inlet, !- Zone Inlet Node Name
118129 Unitary Unit Outlet; !- Setpoint Node or NodeList Name
!only needed if economiser is present in conjunction with unitary equipment...system 3 ASHRAE does not require economiser.
SetpointManager:MixedAir,
118129 AHU Cooling Coil Air Temp Manager, !- Name
Temperature, !- Control Variable
!118129 AHU Air Loop Outlet, !- Reference Setpoint Node Name
118129 Zone Air Node, !- Reference Setpoint Node Name
118129 AHU Mixed Air Outlet, !- Fan Inlet Node Name
118129 AHU Supply Fan Outlet, !- Fan Outlet Node Name
118129 AHU Mixed Air Outlet; !- Setpoint Node or NodeList Name
!118129 AHU Air Loop Outlet; !- Setpoint Node or NodeList Name (not reference node)
Controller:OutdoorAir,
118129 AHU OA Controller,!- Name
118129 AHU Relief Air Outlet, !- Relief Air Outlet Node Name
118129 AHU Air Loop Inlet, !- Return Air Node Name
118129 AHU Mixed Air Outlet, !- Mixed Air Node Name
118129 AHU Outside Air Inlet, !- Actuator Node Name
autosize, !- Minimum Outdoor Air Flow Rate {m3/s}
autosize, !- Maximum Outdoor Air Flow Rate {m3/s}
NoEconomizer, !- Economizer Control Type
ModulateFlow, !- Economizer Control Action Type
25, !- Economizer Maximum Limit Dry-Bulb Temperature {C}
50000, !- Economizer Maximum Limit Enthalpy {J/kg}
, !- Economizer Maximum Limit Dewpoint Temperature {C}
, !- Electronic Enthalpy Limit Curve Name
11, !- Economizer Minimum Limit Dry-Bulb Temperature {C}
NoLockout, !- Lockout Type
FixedMinimum, !- Minimum Limit Type
, !- Minimum Outdoor Air Schedule Name
, !- Minimum Fraction of Outdoor Air Schedule Name
, !- Maximum Fraction of Outdoor Air Schedule Name
; !- Mechanical Ventilation Controller Name
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "n_junk" <n_junk@...> wrote:
>
> Hi Jean,
>
> I've tried to send the file in attachment but I think it failed (I'm still learning how to work with the Yahoo! Groups...).
> I putted it in the "Files"->"_Problem_Submittals"->" EDIT_OF_HVACTemplate-5ZonePackagedVAV.idf ".
>
> Note that the "plenum" temperatures are not controlled, but all the "spaces" temperatures should be controlled (always above 20�C).
> Could the problem be in the VAV terminal damper position?
>
> Thanks in advance!
>
>
>
>
>
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Jean marais" <jeannieboef@> wrote:
> >
> > Post some code snipbits, like the setpoint manager.
> >
> > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "n_junk" <n_junk@> wrote:
> > >
> > > Many thanks for your help, but I still have the same problem.
> > >
> > > I changed the scheduled setpointmanager for the singlezone:heating, but it made no difference.
> > >
> > > What I did was this:
> > > - opened the example file "HVACTemplate-5ZonePackagedVAV.idf" with the Chicago weather file;
> > > - changed the thermostat so that the interior temperature should be between 20-25�C (with the reheat coils active the temperature stays in this limit, so the problem is not from here);
> > > - removed the reheat coils and the cooling coil;
> > > - removed all the lights and electric equipment and most of the people (just to eliminate the influence of internal heating loads);
> > > - changed the heating design temperature from 10�C to 40�C;
> > > - deleted the SetpointManager:Scheduled for Heating and created the SetpointManager:SingleZone:Heating, using the Space3-1 as the control zone name (it's the zone with more heating demands).
> > >
> > > And then the temperatures of Space3-1 (and others) are not hot enough. What else can be wrong? Could the problem be in the setpointmanager: MixedAir ?
> > >
> > > Thanks in advance!
> > >
> > > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Richard Raustad <RRaustad@> wrote:
> > > >
> > > > If you remove the terminal unit heating coils, you can no longer control
> > > > the air loop heating coil at a constant supply air temperature (i.e.,
> > > > using a scheduled temperature set point). Verify how the main heating
> > > > coil is controlled (i'm guessing scheduled) and use a different type of
> > > > set point manager to control it (e.g., SetpointManager:SingleZone:Heating).
> > > >
> > > > On 7/11/2011 7:01 PM, n_junk wrote:
> > > > >
> > > > >
> > > > > Hi! You are refering to "Central Heating Design Supply Air
> > > > > Temperature", right? I forgot to tell that I already had changed it to
> > > > > 20, 30, 40, 50 and even 70�C and none of them hadn't change at all the
> > > > > interior temperature. If I use a high temperature and put again the
> > > > > reheat coils, the rooms sometimes even overheat, but without them the
> > > > > temperatures continues under 20�C.
> > > > >
> > > > > This is really odd, I don't know what is happening.
> > > > >
> > > > > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx
> > > > > <mailto:EnergyPlus_Support%40yahoogroups.com>, Vinay Devanathan
> > > > > <vinay.devanathan@> wrote:
> > > > > >
> > > > > > The main heating coils setpoint temperature will be set such that it
> > > > > only
> > > > > > heats air to a certain temp, (say around 15 - 16 C), so that the reheat
> > > > > > coils can be sized for proper capacity to meet the load. When you
> > > > > remove the
> > > > > > reheat coils, your supply air will obviously be under-heated as the main
> > > > > > heating coil is not sized for that high capacity and will end up
> > > > > providing
> > > > > > supply air at the setpoint temperature. You can look at what the heating
> > > > > > coils design leaving air temperature by viewing the expidf file under
> > > > > > Sizing:System object.
> > > > > >
> > > > > > On Mon, Jul 11, 2011 at 1:02 PM, n_junk@ <
> > > > > > n_junk@> wrote:
> > > > > >
> > > > > > > **
> > > > > > >
> > > > > > >
> > > > > > > Hi!
> > > > > > >
> > > > > > > I'm trying to simulate an existing HVAC system which is similar to
> > > > > a VAV,
> > > > > > > only with heating, without cooling coil or reheat coils. I'm using
> > > > > the HVAC
> > > > > > > Template VAV Packaged.
> > > > > > > The rooms' temperatures stay above 20�C, like I configured in the
> > > > > > > Thermostat, until I remove the reheat coils. When I do that the
> > > > > temperature
> > > > > > > drops under 20�C and only reaches it if there are internal loads.
> > > > > > >
> > > > > > > I have almost everything in autosize, except the maximum flow of
> > > > > the input
> > > > > > > air (but autosize never reaches it, so I think the problem is not from
> > > > > > > there).
> > > > > > >
> > > > > > > To see my problem just open this example file that comes with
> > > > > EnergyPlus:
> > > > > > > HVACTemplate-5ZonePackagedVAV.idf. Then run a simulation and
> > > > > consult the
> > > > > > > evolution of Zone Air Temperature for any of the conditioned zones
> > > > > and see
> > > > > > > that it stays inside the temperatures of the Thermostat. After
> > > > > that go to
> > > > > > > the file, remove the reheat coils of every zone (and deactivate
> > > > > the system
> > > > > > > cooling coil), run the simulation again and compare the
> > > > > temperatures. You'll
> > > > > > > see that now the temperatures stay under the Thermostat limit and
> > > > > only reach
> > > > > > > it when the internal loads harm the room enough.
> > > > > > >
> > > > > > > I'm looking in the expidf file for days and I still don't know what is
> > > > > > > wrong with it. Since I really have to remove the reheat coils,
> > > > > what can I do
> > > > > > > to correct this problem?
> > > > > > >
> > > > > > > Thanks in advance!
> > > > > > >
> > > > > > >
> > > > > > >
> > > > > >
> > > > >
> > > > >
> > > >
> > > > --
> > > > Richard A. Raustad
> > > > Senior Research Engineer
> > > > Florida Solar Energy Center
> > > > University of Central Florida
> > > > 1679 Clearlake Road
> > > > Cocoa, FL 32922-5703
> > > > Phone: (321) 638-1454
> > > > Fax: (321) 638-1439 or 1010
> > > > Visit our web site at: http://www.fsec.ucf.edu
> > > >
> > > > UCF - From Promise to Prominence: Celebrating 40 Years
> > > >
> > >
> >
>
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/