We found most problems from this message are from network connection. Figure 79 in the Input Output Reference is a good example to build a network. In addition, each zone should have two surfaces with leakage components to be exposed to two different boundary conditions.
After double-checking the network connection and the same message still occurs, you may adjust field values listed in the message. These fields are in the AirflowNetwork:SimulationControl. For example, you may increase the values of
convergence tolerance.
If you still have the same problem, please upload the input file and associated weather file. We may take a look.
Hope this helps.
Lixing Gu
From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of kostas ordoumpozanis
Sent: Monday, July 18, 2011 2:55 AM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: [EnergyPlus_Support] problem with air network
Hi, I am trying to simulate a complex building with a AirflowNetwork to calculate the ventilation due to an attrium.
when I am trying to run this AirflowNetwork I get this error ** Severe ** Too many iterations (SOLVZP) in Airflow Network simulation
** Warning ** AirflowNetwork: SOLVER, Changing values for initialization flag, Relative airflow convergence, Absolute airflow convergence, Convergence acceleration limit or Maximum Iteration Number may solve the problem.
any help with this ???
Thanks |