Franck, It is not possible to use two instances of the basement preprocessor while using the “GroundHeatTransfer:Control” object. I would suggest using the basement program twice to generate two sets of temperature profiles (one for each the basement and the crawlspace). When calculating the area-to-perimeter ratio, use the perimeter of each space that is adjacent to the exterior (ignore any perimeter shared by the two zones). Neal Kruis From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of franck_janin Hello, __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.