[EnergyPlus_Support] Re: How to simulate a building having a basement and a crowl space




A related beginner's question. Apologies if this should be a new topic.

In some residential buildings the ventilated crawl space has walls that are above grade and the ground is exposed inside the crawlspace(the "floor" of the crawlspace is bare earth).
The documentation suggests that the basement preprocessor cannot be used for this situation.

How should the ground heat transfer be modeled in this case? Is it safe just to assume the ground temperature will just follow the seasonal variation for the locale.

Thanks,
Andrew.


--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Kruis, Neal" <neal.kruis@...> wrote:
>
> Franck,
> 
> It is not possible to use two instances of the basement preprocessor while using the "GroundHeatTransfer:Control" object. I would suggest using the basement program twice to generate two sets of temperature profiles (one for each the basement and the crawlspace). When calculating the area-to-perimeter ratio, use the perimeter of each space that is adjacent to the exterior (ignore any perimeter shared by the two zones).
> 
> Neal Kruis
> 
> From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of franck_janin
> Sent: Tuesday, July 19, 2011 7:02 AM
> To: EnergyPlus_Support@xxxxxxxxxxxxxxx
> Subject: [EnergyPlus_Support] How to simulate a building having a basement and a crowl space
> 
> 
> 
> Hello,
> 
> I have a building, floor of 180 m², and under it,
> - a ceilar 50m² (2.5 meter height, closed, and slightly ventilated, for wine and potatoes)
> - a crawl space 130 m² (0.8 meter heigh, ventilated).
> 
> I planned to use the Basement program, but is it possible to use 2 instances ? One for ceilar, one for the crawl ?
> 
> I'm not using slab, because it will not give good results, as the crawl is ventilated.
> 
> Any idea ?
> Best regards,
> 
> Franck Janin
>




------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/