Ricahrd, thanks for your reply.

Can the unitary systems aslo be used for humidification and not only
dehumidification? The reason I'm asking is that I'm trying to emulate
the output of a Passive Downdraught Evaporative Cooler which causes a
decrease in dry bulb temperature but an increase in relative humidity.
For reasons that are beyond this message, both objects of the
ZoneCoolTower:Shower and Evaporative Coolers are not suitable for my
model.


--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Richard Raustad
<RRaustad@...> wrote:
>
> The unitary systems can control humidity. Look for AC systems that
have
> this as an input. This is from the
AirLoopHVAC:Unitary:Furnace:HeatCool
> object.
>
> A14, \field Dehumidification Control Type
> \type choice
> \key None
> \key Multimode
> \key CoolReheat
> \default None
> \note None = meet sensible load only
> \note Multimode = activate enhanced dehumidification mode
> \note as needed and meet sensible load. Valid only with
> \note cooling coil type
> CoilSystem:Cooling:DX:HeatExchangerAssisted.
> \note This control mode allows the heat exchanger to be turned
> \note on and off based on the zone dehumidification requirements.
> \note A ZoneControl:Humidistat object is also required.
> \note CoolReheat = cool beyond the dry bulb setpoint.
> \note as required to meet the humidity setpoint. Valid with all
> \note cooling coil types. When a heat exchanger assisted cooling
> \note coil is used, the heat exchanger is locked on at all times.
> \note A ZoneControl:Humidistat object is also required.
>
>
> On 7/20/2011 5:53 PM, omarvelling wrote:
> >
> > Hi all,
> >
> > Is it possible to use a thermostat and humidistat in one zone
> > simultaneously? If so, what type of HVAC should be used? I'm not
> > concerned with the loads but only with the resulting internal
> > conditions of the zone and so an IdealLoadsAirSystem would have
worked
> > fine for me if only controlling the temperature was required.
However,
> > in my case, both temperature and relative humidity need to be
> > controlled. Can anyone help?
> >
> > Thanks a lot,
> > Omar
> >
> >
>
> --
> Richard A. Raustad
> Senior Research Engineer
> Florida Solar Energy Center
> University of Central Florida
> 1679 Clearlake Road
> Cocoa, FL 32922-5703
> Phone: (321) 638-1454
> Fax: (321) 638-1439 or 1010
> Visit our web site at: http://www.fsec.ucf.edu
>
> UCF - From Promise to Prominence: Celebrating 40 Years
>





------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/