Ricahrd, thanks for your reply.
Can the unitary systems aslo be used for humidification
and not only
dehumidification? The reason I'm asking is that I'm trying
to emulate
the output of a Passive Downdraught Evaporative Cooler
which causes a
decrease in dry bulb temperature but an increase in
relative humidity.
For reasons that are beyond this message, both objects of
the
ZoneCoolTower:Shower and Evaporative Coolers are not
suitable for my
model.
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx,
Richard Raustad
<RRaustad@...> wrote:
>
> The unitary systems can control humidity. Look for AC
systems that
have
> this as an input. This is from the
AirLoopHVAC:Unitary:Furnace:HeatCool
> object.
>
> A14, \field Dehumidification Control Type
> \type choice
> \key None
> \key Multimode
> \key CoolReheat
> \default None
> \note None = meet sensible load only
> \note Multimode = activate enhanced dehumidification
mode
> \note as needed and meet sensible load. Valid only
with
> \note cooling coil type
> CoilSystem:Cooling:DX:HeatExchangerAssisted.
> \note This control mode allows the heat exchanger to
be turned
> \note on and off based on the zone dehumidification
requirements.
> \note A ZoneControl:Humidistat object is also
required.
> \note CoolReheat = cool beyond the dry bulb setpoint.
> \note as required to meet the humidity setpoint.
Valid with all
> \note cooling coil types. When a heat exchanger
assisted cooling
> \note coil is used, the heat exchanger is locked on
at all times.
> \note A ZoneControl:Humidistat object is also
required.
>
>
> On 7/20/2011 5:53 PM, omarvelling wrote:
> >
> > Hi all,
> >
> > Is it possible to use a thermostat and
humidistat in one zone
> > simultaneously? If so, what type of HVAC should
be used? I'm not
> > concerned with the loads but only with the
resulting internal
> > conditions of the zone and so an
IdealLoadsAirSystem would have
worked
> > fine for me if only controlling the temperature
was required.
However,
> > in my case, both temperature and relative
humidity need to be
> > controlled. Can anyone help?
> >
> > Thanks a lot,
> > Omar
> >
> >
>
> --