To add to Richards comments, the operating mode schedule changes the fan mode from Continuous to Cycling. A cycling fan cycles on and off to meet the loads.
Make sure the fan is scheduled always on and think about a setback temperature for your thermostat during unoccupied times.
Then use the control mode schedule to change the control mode (0=continuous, 1=cycling...I think) of the fan. You could possibly reference the same schedule here as your occupancy schedule because eplus accepts zeros as zeros and nonzero fractions as 1, when it expects a 0/1 input.
This approach is the alternative to the nightmanager.
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Richard Raustad <RRaustad@...> wrote:
>
> Use the fan operating mode schedule to change modes from day to night.
>
> From the PackagedTerminalHeatPump.idf example file.
>
> ZoneHVAC:PackagedTerminalHeatPump,
> Zone1PTHP, !- Name
> SupplyFanSch; !- Supply Air Fan Operating Mode Schedule Name
>
> Schedule:Compact,
> SupplyFanSch, !- Name
> Fraction, !- Schedule Type Limits Name
> Through: 12/31, !- Field 1
> For: AllDays, !- Field 2
> Until: 7:00,1.0, !- Field 3
> Until: 17:00,0.0, !- Field 3
> Until: 24:00,1.0; !- Field 3
>
>
>
> On 7/21/2011 4:33 PM, riccianop6 wrote:
> >
> > Hi All,
> >
> > I need satisfy the section G3.1.2.4 of Ashrae Standard 90.1-2007.
> >
> > "Supply and return fans shall operate continuously whenever spaces are
> > occupied and shall be cycled to meet heating and cooling loads during
> > unoccupied hours".
> >
> > So, I'm using PTHP system in the building.
> >
> > How can I simulate it if I have no night cycle in this kind of HVAC?
> >
> > Thanks!
> >
> >
>
> --
> Richard A. Raustad
> Senior Research Engineer
> Florida Solar Energy Center
> University of Central Florida
> 1679 Clearlake Road
> Cocoa, FL 32922-5703
> Phone: (321) 638-1454
> Fax: (321) 638-1439 or 1010
> Visit our web site at: http://www.fsec.ucf.edu
>
> UCF - From Promise to Prominence: Celebrating 40 Years
>
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/