A DX coil in an AHU is actually a two stage chiller, in practice.
The low coil temperature condense out the moisture at say 7°C. The inefficient cooling of the coil allows the return air to be cooled to say 18°C. This is used to feed the ducts. By the time the air reaches the diffusers, it is just cool and dry for the room. No other equipment will be needed. ======================== I know the above is not what you wanted. In EPlus, the simulaopn would be a cooler and a reheat system. Dr. Li To: EnergyPlus_Support@xxxxxxxxxxxxxxx From: jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx Date: Fri, 22 Jul 2011 07:48:16 -0400 Subject: RE: [EnergyPlus_Support] Re: Chilled Water at 2 different Temperatures Dear Jean,
I think there was a post several months ago regarding this same issue. I am pretty sure that you cannot model two different setpoint temperatures in the same chilled water loop with E+. Considerations for a workaround: · The Chilled beam object does not object to colder water, nor does the water flow rate change as long as you maintain the proper delta T ? so energy should remain the same o You may want to revise the object parameters to make sure the beam performs the same as with warmer water o I know someone was asking recently in this forum (or Bldg-Sim) about modeling the dewpoint shutoff feature of chilled beams. I did not follow that closely because I felt that most chilled beams systems (in the USA) will use a DOAS that controls humidity, making the dewpoint control less active. Nonetheless, that may be a concern for you. My not-thinking-about-it ?very-long workaround would be to monitor room dewpoint and raise the room setpoint during those periods. · You CAN use two different chilled water loops and may want to do so for your radiant loop. o Ideally, you?d like to take advantage of what is probably a higher return water temp from the radiant loop for chiller efficiency. With two loops, this becomes more difficult, but I think you could make an approximation.
The Building Performance Team
From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Jean marais
Any help on this? How do I set up my loops to deliver 6 degC CW to my AHU, but 18 degC CW to my radiant system. One can only have one PlantLoop, right? If I give my AHU the 18 degC water, I don't get the dehumidification. If I give my ceiling 6 degC water, I get condensation. __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |