RE: [EnergyPlus_Support] Re: Chilled Water at 2 different Temperatures
Dear Jean,
I think there was a post several months ago regarding this same issue. I am pretty sure that you cannot model two different setpoint temperatures in the same chilled water loop with E+.
Considerations for a workaround:
· The Chilled beam object does not object to colder water, nor does the water flow rate change as long as you maintain the proper delta T ? so energy should remain the same
o You may want to revise the object parameters to make sure the beam performs the same as with warmer water
o I know someone was asking recently in this forum (or Bldg-Sim) about modeling the dewpoint shutoff feature of chilled beams. I did not follow that closely because I felt that most chilled beams systems (in the USA) will use a DOAS that controls humidity, making the dewpoint control less active. Nonetheless, that may be a concern for you. My not-thinking-about-it ?very-long workaround would be to monitor room dewpoint and raise the room setpoint during those periods.
·
__._,_.___
Primary EnergyPlus support is found at:
<http://energyplus.helpserve.com>http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
<http://www.energyplus.gov>http://www.energyplus.gov
The group web site is:
<http://groups.yahoo.com/group/EnergyPlus_Support/>http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
<http://geo.yahoo.com/serv?s=97476590/grpId=3387488/grpspId=1705007389/msgId=21076/stime=1311335312>
Your email settings: Individual Email|Traditional
<http://groups.yahoo.com/group/EnergyPlus_Support/join;_ylc=X3oDMTJma2puOXZsBF9TAzk3NDc2NTkwBGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA3N0bmdzBHN0aW1lAzEzMTEzMzUzMTI->Change settings via the Web (Yahoo! ID required)
Change settings via email: <mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx?subject=Email Delivery: Digest>Switch delivery to Daily Digest | Switch to Fully Featured
<http://groups.yahoo.com/group/EnergyPlus_Support;_ylc=X3oDMTJkYzhkNHV1BF9TAzk3NDc2NTkwBGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA2hwZgRzdGltZQMxMzExMzM1MzEy>Visit Your Group | <http://docs.yahoo.com/info/terms/> Yahoo! Groups Terms of Use | <mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscribe> Unsubscribe
__,_._,___