This happens when the system timestep has just shortened, or “downstepped.” E+ has a zone timestep and a system timestep. Here, it has first run a system timestep of 10 minutes (from 8:10 to 8:20), then later decided it should be shorter and repeated a system timestep that starts at 8:10 (from 8:10 to 8:13). Because of this and other iteration/timing issues, you will have a hard time counting up time entirely on your own. So the EMS runtime language includes some built-in variables for time-related data, see Table 2 in the EMS application guide. The built-in variable SystemTimeStep will be useful for your application (e.g. it will have changed from 10/60 to probably 3.3333/60 in your example below). Combine this with the output processing that happens with an EnergyManagementSystem:OutputVariable that is summed and you should be able to get time counted up correctly. Brent From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of dgerome06 Hello, __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.