Wonjun:
The air density is a function of pressure, temperature and humidity ratio
and is calculated using the following equation in the AirflowNetwork model
of EnergyPlus:
rhoair = pb/(287.d0*(tdb+KelvinConv)*(1.d0+1.6077687d0*w))
where
pb = absolute outdoor pressure + indoor gauge pressure
tdb = dry bulb temperature in C
w = humidity ratio
Hope this helps.
Lixing
-----Original Message-----
From: EnergyPlus_Support@xxxxxxxxxxxxxxx
[mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Wonjun
Sent: Tuesday, August 02, 2011 9:51 AM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: [EnergyPlus_Support] I wonder a part of AFN algorithm
Hello fellows
I wonder a part of AFN algorithm, especially the consideration of stack
effect. I have read many text and E+ engineering references, but can't find
the answer of my question.
As you know, bascially the air mass flow is based on the power law equation
like below
air mass flow(M)=C*(dP)^n
the pressure difference of two consecutive nodes (dP) in AFN is (Static P1 +
Dynamic P1 + Stack P1) - (Static P2 + Dynamic P2 + Stack P2).
But generally this kind of Bernoulli's Equation assumes density as the
constant.
If so, Stack P (=rho*g*h) is just the function of height.
Because the density and gravity acceleration are constant.
If so, how that equation considers pressure difference from temperature
difference?
I think AFN consider stack effect in this way but can't sure right or not(I
can't find the detailed assumption from Engineering reference).
If I apply treat the air as an Ideal Gas
Density(rho)=P/RT
Then the density is function of Temperature like this (Because R is constant
and P would be 101.325kPa)
or from the linear assumption
rho=2.7567-0.0053T
then the Stack pressure rho*g*h can consider the pressure difference from
temperature diffrerence also.
I look foward to get an answer of my question.
Thanks in advance.
Best regards.
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to
energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a
high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the
Documentation link and press the "search" button.
Yahoo! Groups Links
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/