Hi Richard,I now specified both and the error went away,
but now I get garbage comming out with humidities of zero
instead of close to 100%. I'm putting the
20110721.epmidf.zip in the problem files area.
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx,
Richard Raustad <RRaustad@...> wrote:
>
> This probably relates to your problem. You tell the
program to chose the
> inlet air humrat, but then specify the outlet air
humrat.
>
> autosize, !- Design Inlet Air Humidity Ratio
{kg-H2O/kg-air}
> 0.0010, !- Design Outlet Air Humidity Ratio Entering
is 0.01178 ,0.0050
> does not work
>
> I would run the program for the sizing period and
report the outdoor T
> and W to see how these values change. That warning
looks like one that
> should provide more information. Alternately you
could specify both or
> autosize both.
>
> On 8/3/2011 8:52 AM, Jean marais wrote:
> >
> > Hi Richard,
> >
> > I've set the coil and it was working until I
upped the entering
> > humidity. I now get:
> > ** Warning ** SizeWaterCoil: Coil="DOAS COOLING
COIL", Cooling Coil
> > has leaving humidity ratio > entering
humidity ratio.
> > ** ~~~ ** ..will be sized for 50% of entering
humidity ratio.
> >
> > EVENTHOUGH entering air from outside has
humidity of 0.01178 and the
> > coil is set to 0.001.
> >
> > SizingPeriod:DesignDay, Summer Design Day in BBI
Terminal, !- Design
> > Day Name
> > 32.0, !- Max Dry-Bulb {C}
> > 10.3, !- Daily Temp Range {C}
> > 0.01178,!21.74, !- Wet-Bulb at Max {C}
gH2O/gDryAir
> > 100761.7, !- Barometric Pressure {N/M**2}
> > 0, !- Wind Speed {m/s}
> > 0, !- Wind Direction {Degrees N=0, S=180}
> > 0.98, !- Clearness {0.0 to 1.1}
> > 0, !- Rain {0-no,1-yes}
> > 0, !- Snow on ground {0-no,1-yes}
> > 15, !- Day of Month
> > 7, !- Month
> > SummerDesignDay, !- Day Type -- used for
schedules
> > 1, !- Daylight Savings Time Indicator
> > HumidityRatio,!WetBulb, !- Type of humidity
temperature Indicator
> > , !- Relative Humidity Day Schedule(not used)
> > , !- Dry-Bulb Temperature Range Modifier Type
(not used)
> > ; !- Dry-Bulb Temperature Range Modifier
Schedule (not used)
> >
> > Coil:Cooling:Water,
> > DOAS Cooling Coil, !- Name
> > 2, !- Availability Schedule Name
> > autosize, !- Design Water Flow Rate of Coil
{m3/s}
> > autosize, !- Design Air Volume Flow Rate {m3/s}
> > 6,!autosize, !- Design Inlet Water Temperature
{C}
> > 32,!autosize, !- Design Inlet Air Temperature
{C}
> > 18,!autosize, !- Design Outlet Air Temperature
{C}
> > autosize, !- Design Inlet Air Humidity Ratio
{kg-H2O/kg-air}
> > !autosize, !- Design Outlet Air Humidity Ratio
{kg-H2O/kg-air}
> > 0.0010, !- Design Outlet Air Humidity Ratio
Entering is 0.01178
> > ,0.0050 does not work
> > DOAS Cooling Coil ChW Inlet, !- Coil Water Inlet
Node
> > DOAS Cooling Coil ChW Outlet, !- Coil Water
Outlet Node
> > DOAS Mixed Air Outlet, !- Air Inlet Node Name
> > DOAS Cooling Coil Air Outlet, !- Air Outlet Node
Name
> > DetailedAnalysis, !- Type of Analysis
> > CrossFlow; !- Heat Exchanger Configuration
> >
> > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx
> >
<mailto:EnergyPlus_Support%40yahoogroups.com>, "Jean
marais"
> > <jeannieboef@> wrote:
> > >
> > > I have the following error:
> > >
> > > ************* Beginning System Sizing
Calculations
> > > ************* Beginning Plant Sizing
Calculations
> > > ** Warning ** In calculating the design
coil UA for
> > Coil:Cooling:Water DOAS COOLING COIL
> > > ** ~~~ ** the apparatus dew-point is below
the coil design inlet
> > water temperature;
> > > ** ~~~ ** the coil bypass factor is
unrealistically large;
> > > ** ~~~ ** the coil outlet design conditions
will be changed to
> > correct the problem.
> > > ** ~~~ ** The initial design conditions
are: Tair,in = 24.4500
> > > ** ~~~ ** Wair,in = 9.478796E-003
> > > ** ~~~ ** Twater,in = 6.0000
> > > ** ~~~ ** Tair,out = 18.0000
> > > ** ~~~ ** Wair,out = 8.000000E-003
> > > ** ~~~ ** The revised design conditions
are: Tair,out = 14.5987
> > > ** ~~~ ** Wair,out = 9.371939E-003
> > >
> > > All my coil inputs possible are autosized.
Zone and System humidity
> > designs are 0.008 (default). My outlet Tair
design is 18 deg (as seen
> > in the error msg.)
> > >
> > > 1) What is going on here exactly?
> > > 2) How can I enter other parameters so that
the error does not occur
> > and no reheat is nessesary.
> > >
> >
> >
>
> --
> Richard A. Raustad