[EnergyPlus_Support] Re: Help with override error
Understood. I'll take a sharper look and get back to the thread later.
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Richard Raustad <RRaustad@...> wrote:
>
> Does your input file include report variables for inlet air T and W, air
> flow rate, coil cooling rate, etc. to use for debugging? Have you
> checked the eio file for any indications of size of this coil? Being a
> developer, I typically do not run files posted on the yahoo groups web
> site since this is a peer-to-peer site.
>
> On 8/3/2011 9:50 AM, Jean marais wrote:
> >
> > Hi Richard,I now specified both and the error went away, but now I get
> > garbage comming out with humidities of zero instead of close to 100%.
> > I'm putting the 20110721.epmidf.zip in the problem files area.
> >
> > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx
> > <mailto:EnergyPlus_Support%40yahoogroups.com>, Richard Raustad
> > <RRaustad@> wrote:
> > >
> > > This probably relates to your problem. You tell the program to chose
> > the
> > > inlet air humrat, but then specify the outlet air humrat.
> > >
> > > autosize, !- Design Inlet Air Humidity Ratio {kg-H2O/kg-air}
> > > 0.0010, !- Design Outlet Air Humidity Ratio Entering is 0.01178 ,0.0050
> > > does not work
> > >
> > > I would run the program for the sizing period and report the outdoor T
> > > and W to see how these values change. That warning looks like one that
> > > should provide more information. Alternately you could specify both or
> > > autosize both.
> > >
> > > On 8/3/2011 8:52 AM, Jean marais wrote:
> > > >
> > > > Hi Richard,
> > > >
> > > > I've set the coil and it was working until I upped the entering
> > > > humidity. I now get:
> > > > ** Warning ** SizeWaterCoil: Coil="DOAS COOLING COIL", Cooling Coil
> > > > has leaving humidity ratio > entering humidity ratio.
> > > > ** ~~~ ** ..will be sized for 50% of entering humidity ratio.
> > > >
> > > > EVENTHOUGH entering air from outside has humidity of 0.01178 and the
> > > > coil is set to 0.001.
> > > >
> > > > SizingPeriod:DesignDay, Summer Design Day in BBI Terminal, !- Design
> > > > Day Name
> > > > 32.0, !- Max Dry-Bulb {C}
> > > > 10.3, !- Daily Temp Range {C}
> > > > 0.01178,!21.74, !- Wet-Bulb at Max {C} gH2O/gDryAir
> > > > 100761.7, !- Barometric Pressure {N/M**2}
> > > > 0, !- Wind Speed {m/s}
> > > > 0, !- Wind Direction {Degrees N=0, S=180}
> > > > 0.98, !- Clearness {0.0 to 1.1}
> > > > 0, !- Rain {0-no,1-yes}
> > > > 0, !- Snow on ground {0-no,1-yes}
> > > > 15, !- Day of Month
> > > > 7, !- Month
> > > > SummerDesignDay, !- Day Type -- used for schedules
> > > > 1, !- Daylight Savings Time Indicator
> > > > HumidityRatio,!WetBulb, !- Type of humidity temperature Indicator
> > > > , !- Relative Humidity Day Schedule(not used)
> > > > , !- Dry-Bulb Temperature Range Modifier Type (not used)
> > > > ; !- Dry-Bulb Temperature Range Modifier Schedule (not used)
> > > >
> > > > Coil:Cooling:Water,
> > > > DOAS Cooling Coil, !- Name
> > > > 2, !- Availability Schedule Name
> > > > autosize, !- Design Water Flow Rate of Coil {m3/s}
> > > > autosize, !- Design Air Volume Flow Rate {m3/s}
> > > > 6,!autosize, !- Design Inlet Water Temperature {C}
> > > > 32,!autosize, !- Design Inlet Air Temperature {C}
> > > > 18,!autosize, !- Design Outlet Air Temperature {C}
> > > > autosize, !- Design Inlet Air Humidity Ratio {kg-H2O/kg-air}
> > > > !autosize, !- Design Outlet Air Humidity Ratio {kg-H2O/kg-air}
> > > > 0.0010, !- Design Outlet Air Humidity Ratio Entering is 0.01178
> > > > ,0.0050 does not work
> > > > DOAS Cooling Coil ChW Inlet, !- Coil Water Inlet Node
> > > > DOAS Cooling Coil ChW Outlet, !- Coil Water Outlet Node
> > > > DOAS Mixed Air Outlet, !- Air Inlet Node Name
> > > > DOAS Cooling Coil Air Outlet, !- Air Outlet Node Name
> > > > DetailedAnalysis, !- Type of Analysis
> > > > CrossFlow; !- Heat Exchanger Configuration
> > > >
> > > > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx
> > <mailto:EnergyPlus_Support%40yahoogroups.com>
> > > > <mailto:EnergyPlus_Support%40yahoogroups.com>, "Jean marais"
> > > > <jeannieboef@> wrote:
> > > > >
> > > > > I have the following error:
> > > > >
> > > > > ************* Beginning System Sizing Calculations
> > > > > ************* Beginning Plant Sizing Calculations
> > > > > ** Warning ** In calculating the design coil UA for
> > > > Coil:Cooling:Water DOAS COOLING COIL
> > > > > ** ~~~ ** the apparatus dew-point is below the coil design inlet
> > > > water temperature;
> > > > > ** ~~~ ** the coil bypass factor is unrealistically large;
> > > > > ** ~~~ ** the coil outlet design conditions will be changed to
> > > > correct the problem.
> > > > > ** ~~~ ** The initial design conditions are: Tair,in = 24.4500
> > > > > ** ~~~ ** Wair,in = 9.478796E-003
> > > > > ** ~~~ ** Twater,in = 6.0000
> > > > > ** ~~~ ** Tair,out = 18.0000
> > > > > ** ~~~ ** Wair,out = 8.000000E-003
> > > > > ** ~~~ ** The revised design conditions are: Tair,out = 14.5987
> > > > > ** ~~~ ** Wair,out = 9.371939E-003
> > > > >
> > > > > All my coil inputs possible are autosized. Zone and System humidity
> > > > designs are 0.008 (default). My outlet Tair design is 18 deg (as seen
> > > > in the error msg.)
> > > > >
> > > > > 1) What is going on here exactly?
> > > > > 2) How can I enter other parameters so that the error does not
> > occur
> > > > and no reheat is nessesary.
> > > > >
> > > >
> > > >
> > >
> > > --
> > > Richard A. Raustad
> > > Senior Research Engineer
> > > Florida Solar Energy Center
> > > University of Central Florida
> > > 1679 Clearlake Road
> > > Cocoa, FL 32922-5703
> > > Phone: (321) 638-1454
> > > Fax: (321) 638-1439 or 1010
> > > Visit our web site at: http://www.fsec.ucf.edu
> > >
> > > UCF - From Promise to Prominence: Celebrating 40 Years
> > >
> >
> >
>
> --
> Richard A. Raustad
> Senior Research Engineer
> Florida Solar Energy Center
> University of Central Florida
> 1679 Clearlake Road
> Cocoa, FL 32922-5703
> Phone: (321) 638-1454
> Fax: (321) 638-1439 or 1010
> Visit our web site at: http://www.fsec.ucf.edu
>
> UCF - From Promise to Prominence: Celebrating 40 Years
>
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/