I have not look at the IDF yet.
I did mentioned to you last time that the same storage Tank may have to appear twice in both the demand loop and the supply loop. One for discharging, and one for charging. This is in accordance to the example file. The use side is connected to the demand loop. The source side is connected to the supply loop. The other possibility of the error message is the ordering or naming of the branches in the branch list. They must be listed according to the connection sequence in the loop, starting from the supply loop inlet node, normally a pipe with an pump object. Dr. Li To: EnergyPlus_Support@xxxxxxxxxxxxxxx From: zqianmin@xxxxxxxxx Date: Wed, 3 Aug 2011 09:25:26 -0700 Subject: [EnergyPlus_Support] Help on error msg about thermal tank doesn't match plantloop
Hello All, I got an error msg and could not find the problem, any one could help me out please?
It is a TES tank to cooling tower and radiant cooling system. My idf file is attached. Thanks a lot. Qianmin
************* Beginning Zone Sizing Calculations ** Severe ** ThermalStorage:ChilledWater:Stratified = TES TANK: ** ~~~ ** ...match to PlantLoop not found.
** ~~~ ** ...could not find matching PlantLoop for BranchList=CONDENSER DEMAND BRANCHES. ** Fatal ** Errors found in getting ThermalStorage:ChilledWater:Stratified input. Preceding condition causes termination.
...Summary of Errors that led to program termination: ..... Reference severe error count=1 ..... Last severe error=ThermalStorage:ChilledWater:Stratified = TES TANK: ************* Warning: Node connection errors not checked - most system input has not been read (see previous warning).
************* Fatal error -- final processing. Program exited before simulations began. See previous error messages.
__._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.