I'm going to try modified the RadLoTempCFloHeatCool.idf, move all the condenser loop related objects to plant loop objects, and see if there is any different in the results. 

I will change all the equipment using autosize after it to check the results.

The only different I can tell is the "Loop temperature setpoint node name or reference", there are two additional selection of "air and ground" in condenser loop object. It says this node is used by loop manager to maintain the temperature. So that is something considering bypass pipe, right? 
Because "air" and "ground" temperature are from weather file, not a temperature we could define in schedule, so they are the special thing in condenser loop object. 

After I changed the condenser loop to plant loop, I have to choose condenser loop outlet node instead of Air to be the reference node. I'm not sure if this change will bring a big difference theoretically.

On Thu, Aug 4, 2011 at 10:46 AM, YuanLu Li <yli006@xxxxxxxxxxx> wrote:
 

I expended the HVACTemplate-5ZoneWaterToAirHeatPumpTowerBoiler.idf  in the exampleFiles directory.

The tower and water section is in the attached text file.

 

The templates are expanded to many branches and control objects.

 

The hot and cold water was applied to the heat pump.  In your case, the hot and cold water will be applied directly to the zone coils.

 

I do not know whether you can do this direct substitution.

 

 Dr. Li  

 


To: EnergyPlus_Support@xxxxxxxxxxxxxxx
From: zqianmin@xxxxxxxxx
Date: Thu, 4 Aug 2011 10:01:29 -0700
Subject: Re: [EnergyPlus_Support] Condenser Loop and Cooling Tower


 
I just tried using plant loop instead of condenser loop. and it works!! generate the correct .svg file.
I didn't use any object related to condenser loop.
The reason I did that because it gave me this error before and seem I can't put tank in condenser loop demand side.

ThermalStorage:ChilledWater:Stratified = TES TANK:
   **   ~~~   ** ...match to PlantLoop not found.
   **   ~~~   ** ...could not find matching PlantLoop for BranchList=CONDENSER DEMAND BRANCHES.



On Thu, Aug 4, 2011 at 9:51 AM, Karen Walkerman <kwalkerman@xxxxxxxxx> wrote:
 


"Why I can't use plant loop instead of condenser loop? "

...because whoever wrote the software made it that way...


On Thursday, August 4, 2011, Qianmin Zhang <zqianmin@xxxxxxxxx> wrote:
>  
>
> So I have to use condenser loop to define the loop with cooling tower?
>
> Why I can't use plant loop instead of condenser loop? Condenser loop has less input than plant loop. Thank you for your response.
> Qianmin
>
> On Thu, Aug 4, 2011 at 8:58 AM, Richard Raustad <RRaustad@xxxxxxxxxxxx> wrote:
>>
>>  
>>
>> Yes, use the condenser loop object. In addition to the tower, you should also be connecting some equipment in the plant loop to this condenser loop.  The software treats these loops separately through calling subroutines in the program.
>>
>> On 8/4/2011 11:34 AM, Qianmin Zhang wrote:
>>
>>  
>>
>> Do I have to use the object of condenser loop if there is a cooling tower in the plant?
>>
>> What the purpose to separate the condenser loop from all other plant loop in energyplus?
>> In input and output reference, both plant loop and condenser loop have similar structure diagram (fig 62 and fig. 63)
>>
>> --
>> Richard A. Raustad
>> Senior Research Engineer
>> Florida Solar Energy Center
>> University of Central Florida
>> 1679 Clearlake Road
>> Cocoa, FL  32922-5703
>> Phone:   (321) 638-1454 <tel:%28321%29%20638-1454>
>> Fax:     (321) 638-1439 <tel:%28321%29%20638-1439> or 1010

>> Visit our web site at: http://www.fsec.ucf.edu
>>
>> UCF - From Promise to Prominence: Celebrating 40 Years
>
>






__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___