Re: [EnergyPlus_Support] Creating a Shadowing Transmittance Schedule for a overhang





Since you will need to set the schedule (0 is opaque, 1 is transparent) dependent on other conditions, you will need to use the EMS feature (see example file EMSCustomSchedule).

As to the schedule -- it's just like any other schedule.


At 08:26 AM 8/8/2011, pietsor wrote:
Hi everyone!

I have a small problem.
I am simulating a building with a shading overhang above a window.
I want this overhang not to be fixed but opening and closing depending on BOTH INSIDE TEMPERATURE (21°C) and EXT SOLAR INCIDENT.

So what I want is that the overhang closes with Inside Temperature passing 21°C AND Solar Incident above certain value (that I dont know yet).

In the manual of EnergyPlus i read that i can use a Shadowing Transmittance Schedule in my Shading zone Object.

I just dont know how to make this shedule, as normal schedules are varying with time, not with values of Temperature and Solar Incident.
I know the output value of this schedule needs to be between 0.0 and 1.0 (transmittance of the overhang) depending the other values, but how do enter them?

Can anyone help me with the code for this shedule?

You would make me very happy :)

Greeting from Belgium

Pieter



------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/


__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___