[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

[EnergyPlus_Support] AFN - trouble spotting



Hi all, please help. I'm inserting an exhaust fan.

Error:
   ** Severe  ** ValidateExhaustFanInput: The number of AirflowNetwork:MultiZone:Component:ZoneExhaustFan is not equal to the number of Fan:ZoneExhaust fans defined in ZoneHVAC:EquipmentConnections
   **   ~~~   ** The number of AirflowNetwork:MultiZone:Component:ZoneExhaustFan is 2
   **   ~~~   ** The number of Zone exhaust fans defined in ZoneHVAC:EquipmentConnections is 5
   ** Severe  ** AirflowNetwork:MultiZone:Component:ZoneExhaustFan  = 118204 XFAN1 WC is defined and never used.
   ** Severe  ** AirflowNetwork:MultiZone:Component:ZoneExhaustFan  = 118204 XFAN2 WC is defined and never used.

Input:
  ZoneHVAC:EquipmentConnections,
    118204,                  !- Zone Name
    118204Equipment,         !- Zone Conditioning Equipment List Name
    118204 Zone Equip Inlet, !- Zone Air Inlet Node or NodeList Name
    118204 WC Exhaust Air Nodes List,                        !- Zone Air Exhaust Node or NodeList Name
    118204 Zone Air Node,    !- Zone Air Node Name
    118204 Return Outlet;    !- Zone Return Air Node Name
    
  NodeList,
    118204 WC Exhaust Air Nodes List,
    118204 WC Exhaust Air Node1,
    118204 WC Exhaust Air Node2; !- Node ID    

  AirflowNetwork:MultiZone:Component:ZoneExhaustFan,
  118204 XFan1 WC, !- Name 
  0.01, !- Air Mass Flow Coefficient When the Zone Exhaust Fan is Off at Reference Conditions {kg/s}
  0.667; !- Air Mass Flow Exponent When the Zone Exhaust Fan is Off{dimensionless}
  ReferenceCrackConditions; !- Reference Crack Conditions
  
  AirflowNetwork:MultiZone:Component:ZoneExhaustFan,
  118204 XFan2 WC, !- Name 
  0.01, !- Air Mass Flow Coefficient When the Zone Exhaust Fan is Off at Reference Conditions {kg/s}
  0.667; !- Air Mass Flow Exponent When the Zone Exhaust Fan is Off{dimensionless}
  ReferenceCrackConditions; !- Reference Crack Conditions

  !JMM change equipment type in Equipment List

  ZoneHVAC:EquipmentList,
    118204Equipment,         !- Name
    AirTerminal:SingleDuct:Uncontrolled,  !- Zone Equipment 1 Object Type
    118204AirTerminal:SingleDuct:Uncontrolled,  !- Zone Equipment 1 Name
    2,                       !- Zone Equipment 1 Cooling Sequence
    2,                       !- Zone Equipment 1 Heating or No-Load Sequence
    ZoneHVAC:LowTemperatureRadiant:VariableFlow,  !- Zone Equipment 2 Object Type
    118204Baseboard Heat,    !- Zone Equipment 2 Name
    1,                       !- Zone Equipment 2 Cooling Sequence
    1,                                                       !- Zone Equipment 2 Heating or No-Load Sequence 
    Fan:ZoneExhaust,                                         !- Zone Equipment 2 Object Type
    118204 XFan1 WC,                            !- Zone Equipment 2 Name
    3,                                                       !- Zone Equipment 2 Cooling Sequence
    3,                                                       !- Zone Equipment 2 Heating or No-Load Sequence 
    Fan:ZoneExhaust,                                         !- Zone Equipment 2 Object Type
    118204 XFan2 WC,                            !- Zone Equipment 3 Name
    4,                                                       !- Zone Equipment 3 Cooling Sequence
    4;                                                       !- Zone Equipment 3 Heating or No-Load Sequence
    
    !!!!!!!!!!!!!!!Exhaust Fan WC Start

  Fan:ZoneExhaust,
    118204 XFan1 WC,     !- Name WC Exhaust Fan
    HVACTemplate-Always 1,   !- Availability Schedule Name
    0.7,                     !- Fan Efficiency
    142,                     !- Pressure Rise {Pa}
    0.0166666,            !- Mech ventilation (m3/s)      60 m³/h
    118204 WC Exhaust Air Node1,   !- Air Inlet Node Name
    118204 WC Outside Node1,  !- Air Outlet Node Name
    WC Exhaust;         !- End-Use Subcategory
!!!!!!!!!!!!!!!Exhaust Fan WC End

  Fan:ZoneExhaust,
    118204 XFan2 WC,     !- Name WC Exhaust Fan
    HVACTemplate-Always 1,   !- Availability Schedule Name
    0.7,                     !- Fan Efficiency
    142,                     !- Pressure Rise {Pa}
    0.0166666,            !- Mech ventilation (m3/s)      60 m³/h
    118204 WC Exhaust Air Node2,   !- Air Inlet Node Name
    118204 WC Outside Node2,  !- Air Outlet Node Name
    WC Exhaust;         !- End-Use Subcategory
!!!!!!!!!!!!!!!Exhaust Fan WC End



------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/