Please HELP
Severe ** AirflowNetwork:MultiZone:Component:ZoneExhaustFan = 118204 XFAN1 WC is defined and never used.
ZoneHVAC:EquipmentConnections,
118403, !- Zone Name
118403Equipment, !- Zone Conditioning Equipment List Name
118403 Zone Equip Inlet, !- Zone Air Inlet Node or NodeList Name
118403 WC Exhaust Air Nodes List, !- Zone Air Exhaust Node or NodeList Name
118403 Zone Air Node, !- Zone Air Node Name
118403 Return Outlet; !- Zone Return Air Node Name
NodeList,
118403 WC Exhaust Air Nodes List,
118403 WC Exhaust Air Node1; !- Node ID
AirflowNetwork:MultiZone:Surface,
R_118403_5_0_0, !- Surface Name
118403 WC, !- Leakage Component Name
118403 Horizontal, !- External Node Name
1.0; !- Window/Door Opening Factor, or Crack Factor {dimensionless}
!Node Required per Surface
AirflowNetwork:MultiZone:ExternalNode,
118403 Horizontal,!- Name
5.00, !- External Node Height {m}
HorizontalWPC;!- Wind Pressure Coefficient Values Object Name
AirflowNetwork:MultiZone:Surface:EffectiveLeakageArea,
118403 WC, !- Name
0.002, !- Effective Leakage Area {m2}
1.0, !- Discharge Coefficient {dimensionless}
4.0, !- Reference Pressure Difference {Pa}
0.667; !- Air Mass Flow Exponent {dimensionless}
AirflowNetwork:MultiZone:Component:ZoneExhaustFan,
118403 XFan1 WC, !- Name
0.01, !- Air Mass Flow Coefficient When the Zone Exhaust Fan is Off at Reference Conditions {kg/s}
0.667; !- Air Mass Flow Exponent When the Zone Exhaust Fan is Off{dimensionless}
ReferenceCrackConditions; !- Reference Crack Conditions
ZoneHVAC:EquipmentList,
118403Equipment, !- Name
AirTerminal:SingleDuct:Uncontrolled, !- Zone Equipment 1 Object Type
118403AirTerminal:SingleDuct:Uncontrolled, !- Zone Equipment 1 Name
1, !- Zone Equipment 1 Cooling Sequence
1, !- Zone Equipment 2 Heating or No-Load Sequence
Fan:ZoneExhaust, !- Zone Equipment 2 Object Type
118403 XFan1 WC, !- Zone Equipment 2 Name
2, !- Zone Equipment 2 Cooling Sequence
2;
!!!!!!!!!!!!!!!Exhaust Fan WC Start
Fan:ZoneExhaust,
118403 XFan1 WC, !- Name WC Exhaust Fan
HVACTemplate-Always 1, !- Availability Schedule Name
0.7, !- Fan Efficiency
142, !- Pressure Rise {Pa}
0.0166666, !- Mech ventilation (m3/s) 60 m³/h
118403 WC Exhaust Air Node1, !- Air Inlet Node Name
118403 WC Outside Node1, !- Air Outlet Node Name
WC Exhaust; !- End-Use Subcategory
!!!!!!!!!!!!!!!Exhaust Fan WC End
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/