I think you may miss an AirflowNetwork:MultiZone:Surface object to define “118403 XFan1 WC” as Leakage Component Name. Here are examples to defined ZoneExhaust fans extracted from AirflowNetwork_MultiZone_SmallOffice.idf, one of example input files. AirflowNetwork:MultiZone:Surface, Zn003:Wall003, !- Surface Name Zone3 Exhaust Fan, !- Leakage Component Name EFacade, !- External Node Name 1.0; !- Window/Door Opening Factor, or Crack Factor {dimensionless} AirflowNetwork:MultiZone:Component:ZoneExhaustFan, Zone3 Exhaust Fan, !- Name 0.01, !- Air Mass Flow Coefficient When the Zone Exhaust Fan is Off at Reference Conditions {kg/s} 0.667; !- Air Mass Flow Exponent When the Zone Exhaust Fan is Off {dimensionless} ZoneHVAC:EquipmentList, Zone3Equipment, !- Name AirTerminal:SingleDuct:Uncontrolled, !- Zone Equipment 1 Object Type Zone3DirectAir, !- Zone Equipment 1 Name 1, !- Zone Equipment 1 Cooling Sequence 1, !- Zone Equipment 1 Heating or No-Load Sequence Fan:ZoneExhaust, !- Zone Equipment 2 Object Type Zone3 Exhaust Fan, !- Zone Equipment 2 Name 2, !- Zone Equipment 2 Cooling Sequence 2; !- Zone Equipment 2 Heating or No-Load Sequence Fan:ZoneExhaust, Zone3 Exhaust Fan, !- Name FanAndCoilAvailSched, !- Availability Schedule Name 0.7, !- Fan Efficiency 500, !- Pressure Rise {Pa} 0.01, !- Maximum Flow Rate {m3/s} Zone3 Exhaust Node, !- Air Inlet Node Name Zone3 Exhaust Fan Outlet Node, !- Air Outlet Node Name Zone Exhaust; !- End-Use Subcategory ZoneHVAC:EquipmentConnections, NORTH ZONE, !- Zone Name Zone3Equipment, !- Zone Conditioning Equipment List Name Zone3Inlets, !- Zone Air Inlet Node or NodeList Name Zone3 Exhaust Node, !- Zone Air Exhaust Node or NodeList Name Zone 3 Node, !- Zone Air Node Name Zone 3 Outlet Node; !- Zone Return Air Node Name Hope this helps. Lixing From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Linda Lawrie
Please HELP __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |