[EnergyPlus_Support] Re: Inserting Fan:ZoneExhaust into AFN zone
Dear Group,
I have split my roof detailed areas so that each fan:zoneexhaust is on its
own surface with own crack surface and properties defined. Still I get the
same error.
I have uploaded my actual file with revised objects, to the help desk...but for the rest of you there's a snip bit below.
I have included following AFN things:
- seperate BuildingSurface:Detailed objects for the fan roof penetrations
- seperate AirflowNetwork:MultiZone:Surface for each fan roof penetration
- seperate AirflowNetwork:MultiZone:ExternalNode nodes for each fan
- seperate AirflowNetwork:MultiZone:Component:ZoneExhaustFan for each fan
- new AirflowNetwork:MultiZone:Surface:EffectiveLeakageArea
- new AirflowNetwork:MultiZone:WindPressureCoefficientValues
- new AirflowNetwork:MultiZone:ReferenceCrackConditions
** Severe ** AirflowNetwork:MultiZone:Component:ZoneExhaustFan = 118204
XFAN1 WC is defined and never used.
** Severe ** AirflowNetwork:MultiZone:Component:ZoneExhaustFan = 118204
XFAN2 WC is defined and never used.
** Severe ** AirflowNetwork:MultiZone:Component:ZoneExhaustFan = 118386
XFAN1 WC is defined and never used.
** Severe ** AirflowNetwork:MultiZone:Component:ZoneExhaustFan = 118386
XFAN2 WC is defined and never used.
** Severe ** AirflowNetwork:MultiZone:Component:ZoneExhaustFan = 118403
XFAN1 WC is defined and never used.
Ticket Details
> ===================
> Ticket ID: 4618
> Department: General
> Priority: Medium
> Status: Open
ZoneHVAC:EquipmentConnections,
118204, !- Zone Name
118204Equipment, !- Zone Conditioning Equipment List Name
118204 Zone Equip Inlet, !- Zone Air Inlet Node or NodeList Name
118204 WC Exhaust Air Nodes List, !- Zone Air Exhaust Node or NodeList Name
118204 Zone Air Node, !- Zone Air Node Name
118204 Return Outlet; !- Zone Return Air Node Name
NodeList,
118204 WC Exhaust Air Nodes List,
118204 WC Exhaust Air Node1,
118204 WC Exhaust Air Node2; !- Node ID
AirflowNetwork:MultiZone:WindPressureCoefficientValues,
HorizontalWPC, !- Name
Cp Data, !- AirflowNetwork:MultiZone:WindPressureCoefficientArray Name
0.00, !- Wind Pressure Coefficient Value 1 {dimensionless}
0.00, !- Wind Pressure Coefficient Value 2 {dimensionless}
0.00, !- Wind Pressure Coefficient Value 3 {dimensionless}
0.00, !- Wind Pressure Coefficient Value 4 {dimensionless}
0.00, !- Wind Pressure Coefficient Value 5 {dimensionless}
0.00, !- Wind Pressure Coefficient Value 6 {dimensionless}
0.00, !- Wind Pressure Coefficient Value 7 {dimensionless}
0.00; !- Wind Pressure Coefficient Value 8 {dimensionless}
AirflowNetwork:MultiZone:Surface,
R_118204_6_1_7_xfan1, !- Surface Name
118204 WC, !- Leakage Component Name
R_118204_6_1_7_xfan1 ODA Node, !- External Node Name
1.0; !- Window/Door Opening Factor, or Crack Factor {dimensionless}
!Node Required per Surface
AirflowNetwork:MultiZone:ExternalNode,
R_118204_6_1_7_xfan1 ODA Node,!- Name
5.00, !- External Node Height {m}
HorizontalWPC;!- Wind Pressure Coefficient Values Object Name
AirflowNetwork:MultiZone:Surface,
R_118204_6_1_8_xfan2, !- Surface Name
118204 WC, !- Leakage Component Name
R_118204_6_1_8_xfan2 ODA Node, !- External Node Name
1.0; !- Window/Door Opening Factor, or Crack Factor {dimensionless}
!Node Required per Surface
AirflowNetwork:MultiZone:ExternalNode,
R_118204_6_1_8_xfan2 ODA Node,!- Name
5.00, !- External Node Height {m}
HorizontalWPC;!- Wind Pressure Coefficient Values Object Name
AirflowNetwork:MultiZone:Surface:EffectiveLeakageArea,
118204 WC, !- Name
0.002, !- Effective Leakage Area {m2}
1.0, !- Discharge Coefficient {dimensionless}
4.0, !- Reference Pressure Difference {Pa}
0.667; !- Air Mass Flow Exponent {dimensionless}
AirflowNetwork:MultiZone:ReferenceCrackConditions,
ReferenceCrackConditions,!- Name
20.0, !- Reference Temperature {C}
101325, !- Reference Barometric Pressure {Pa}
0.0; !- Reference Humidity Ratio {kg/kg}
AirflowNetwork:MultiZone:Component:ZoneExhaustFan,
118204 XFan1 WC, !- Name
0.01, !- Air Mass Flow Coefficient When the Zone Exhaust Fan is Off at Reference Conditions {kg/s}
0.667, !- Air Mass Flow Exponent When the Zone Exhaust Fan is Off{dimensionless}
ReferenceCrackConditions; !- Reference Crack Conditions
AirflowNetwork:MultiZone:Component:ZoneExhaustFan,
118204 XFan2 WC, !- Name
0.01, !- Air Mass Flow Coefficient When the Zone Exhaust Fan is Off at Reference Conditions {kg/s}
0.667, !- Air Mass Flow Exponent When the Zone Exhaust Fan is Off{dimensionless}
ReferenceCrackConditions; !- Reference Crack Conditions
ZoneHVAC:EquipmentList,
118204Equipment, !- Name
AirTerminal:SingleDuct:Uncontrolled, !- Zone Equipment 1 Object Type
118204AirTerminal:SingleDuct:Uncontrolled, !- Zone Equipment 1 Name
1, !- Zone Equipment 1 Cooling Sequence
1, !- Zone Equipment 2 Heating or No-Load Sequence
Fan:ZoneExhaust, !- Zone Equipment 2 Object Type
118204 XFan1 WC, !- Zone Equipment 2 Name
2, !- Zone Equipment 2 Cooling Sequence
2, !- Zone Equipment 2 Heating or No-Load Sequence
Fan:ZoneExhaust, !- Zone Equipment 2 Object Type
118204 XFan2 WC, !- Zone Equipment 3 Name
3, !- Zone Equipment 3 Cooling Sequence
3; !- Zone Equipment 3 Heating or No-Load Sequence
!!!!!!!!!!!!!!!Exhaust Fan WC Start
Fan:ZoneExhaust,
118204 XFan1 WC, !- Name WC Exhaust Fan
HVACTemplate-Always 1, !- Availability Schedule Name
0.7, !- Fan Efficiency
142, !- Pressure Rise {Pa}
0.0166666, !- Mech ventilation (m3/s) 60 m³/h
118204 WC Exhaust Air Node1, !- Air Inlet Node Name
118204 WC Outside Node1, !- Air Outlet Node Name
WC Exhaust; !- End-Use Subcategory
!!!!!!!!!!!!!!!Exhaust Fan WC End
Fan:ZoneExhaust,
118204 XFan2 WC, !- Name WC Exhaust Fan
HVACTemplate-Always 1, !- Availability Schedule Name
0.7, !- Fan Efficiency
142, !- Pressure Rise {Pa}
0.0166666, !- Mech ventilation (m3/s) 60 m³/h
118204 WC Exhaust Air Node2, !- Air Inlet Node Name
118204 WC Outside Node2, !- Air Outlet Node Name
WC Exhaust; !- End-Use Subcategory
!!!!!!!!!!!!!!!Exhaust Fan WC End
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/