|
Hi,Aditya
I found an extra line at the end of the template PTAC ====================== HVACTemplate:Zone:PTAC, ZONE ONE, !- Zone Name Single Zone, !- Template Thermostat Name autosize, !- Cooling Supply Air Flow Rate {m3/s} autosize, !- Heating Supply Air Flow Rate {m3/s} , !- No Load Supply Air Flow Rate {m3/s} , !- Zone Heating Sizing Factor , !- Zone Cooling Sizing Factor Flow/Person, !- Outdoor Air Method 0.00944, !- Outdoor Air Flow Rate per Person {m3/s} , !- Outdoor Air Flow Rate per Zone Floor Area {m3/s-m2} , !- Outdoor Air Flow Rate per Zone {m3/s} , !- System Availability Schedule Name Cycling, !- Supply Fan Operating Mode Schedule Name DrawThrough, !- Supply Fan Placement 0.7, !- Supply Fan Total Efficiency 75, !- Supply Fan Delta Pressure {Pa} 0.9, !- Supply Fan Motor Efficiency SingleSpeedDX, !- Cooling Coil Type , !- Cooling Coil Availability Schedule Name autosize, !- Cooling Coil Rated Capacity {W} 0.8, !- Cooling Coil Rated Sensible Heat Ratio 3, !- Cooling Coil Rated COP {W/W} Electric, !- Heating Coil Type , !- Heating Coil Availability Schedule Name autosize, !- Heating Coil Capacity {W} 0.8, !- Gas Heating Coil Efficiency , !- Gas Heating Coil Parasitic Electric Load {W} ; !- Dedicated Outdoor Air System Name =========================== Remove the last line and change the preceding 'comma' into a 'semicolon'. The sever error should disappear. If this is a fix in the version update. I have no idea how this line was added, as I did not use the IDFeditor to make the changes. Dr. Li To: EnergyPlus_Support@xxxxxxxxxxxxxxx From: adityaravi87@xxxxxxxxx Date: Tue, 16 Aug 2011 09:58:12 -0700 Subject: Re: [EnergyPlus_Support] Re: Setting the HVAC ON/OFF cycle Dr.Li, I ran the file you had sent me but there seems to be a severe error and hence the simulation was incomplete. Following was the error message I got: Program Version,EnergyPlus 6.0.0.023, 8/16/2011 12:55 PM,IDD_Version 6.0.0.023 ** Severe ** Output:PreprocessorMessage="ExpandObjects" has the following Fatal conditions: **
~~~ ** SEVERE: Too many fields were found for the object: HVACTemplate:Zone:PTAC ** ~~~ ** ** ~~~ ** Number expected=[27] ** ~~~ ** Number found=[28] ** Fatal ** Preprocessor condition(s) cause termination. ...Summary of Errors that led to program termination: ..... Reference severe error count=1 ..... Last severe error=Output:PreprocessorMessage="ExpandObjects" has the following Fatal conditions: ************* Warning: Node connection errors not checked - most system input has not been read (see previous warning). ************* Fatal error -- final processing. Program exited before simulations began. See previous error messages. *************
EnergyPlus Warmup Error Summary. During Warmup: 0 Warning; 0 Severe Errors. ************* EnergyPlus Sizing Error Summary. During Sizing: 0 Warning; 0 Severe Errors. ************* EnergyPlus Terminated--Fatal Error Detected. 0 Warning; 1 Severe Errors; Elapsed Time=00hr 00min 1.31sec I am not sure what changes I need to do to correct them. Also by the output what I meant was, if I could see the zone temp fluctuate between the
set point and the set back of say 1 deg C. So when we reach the set point the compressor should go OFF and I should be able to monitor how the room/zone temp varies. Then once again on reaching the set point, compressor kicks ON and then I should be able to see the variations in the zone temp. Regards, Aditya From: YuanLu Li <yli006@xxxxxxxxxxx> To: Linda Lawrie <energyplus_support@xxxxxxxxxxxxxxx> Sent: Monday, August 15, 2011 4:48 PM Subject: RE: [EnergyPlus_Support] Re: Setting the HVAC ON/OFF cycle
Hi, Aditya
If you are not an experienced software program, I do not think you can handle the EMS in EPlus. It is a software debugging tool modified for variable viewing and changing. If you run the exercises in the Getting Started Document, you will have learned how to use theremostat and other schedules. ON/OFF in HVAC is done using a theremostat control. There is nothing special about it. The part that is confusing is that the VAV system does not use the zone thermostat cirectly. Three or four more parameters are used to allow the zone thermostat to control the variable damper in the zone, and turning on the reheat system and adjust the OA damper. So stay away from VAV. The part that is difficult for a beginner to do is to want the ON/OFF at a precise setback of 1 or 2°C. ========================= Theremostat type 1 is for heating with SB, Type 2 is cooling with SB. Tpye 3 is one set point for both heating and cooling. Because these types do not have a dead band, you cannot activate them at the same time. In another word, you will have a Summer and Winter period defined for these schedules to be active. Thermostat type 4 defines two bands, one for cooling and one for heating. They do not overlap. The space between the band is the dead band where neither cooling nor the heating system would be turned ON. This is very useful for places where the transition from Summer to Winter is not well defined. You may want heating at the night and cooling during the day time. Run any example without the VAV will provide you with a running model. ====================== The zone occupancy and equipment schedules are independent of the thermostat schedules. I do not know what you meant by "to get the simulation output in the format I had written in this post". If you are referring to a building green certificate report. You have to do a lot more than just simmulating a system. I know how to do it, but I do not want to be involved to write one, because I do not have the reference documents. ================= If I can retrieve your earlier IDF, I will correct it and mail it to you. Dr. Li To: EnergyPlus_Support@xxxxxxxxxxxxxxx From: adityaravi87@xxxxxxxxx Date: Mon, 15 Aug 2011 17:08:49 +0000 Subject: [EnergyPlus_Support] Re: Setting the HVAC ON/OFF cycle
Dr.Li,
Thank you for the time. Well I had some schedules put up for the equipment and Lights. Also I have included some occupancy schedule in my idf. So the warnings are now associated with these inputs only. I changed my CLGSP sch and HTGSP sch to the simple example one which you have suggested. If you can now tell me what is type4 Thermostat and how I can use it and also how to choose or set the on/off fan instead of the constant fan, I can make the changes and run the simulation. Like I mentioned my final motive is to achieve a ON/OFF schedule for the HVAC. I was also given a suggestion to look into EMS documentation which I am doing right now. It will be of great help if you can modify my IDF and send me the file with pointers explaining how the schedule works. I need to get the simulation output in the format I had written in this post. Please guide me through it. Sincerely, Aditya --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, YuanLu Li <yli006@...> wrote: > > > > > Previous mail removed.
__._,_.___
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button. .
__,_._,___
|