Re: [EnergyPlus_Support] Heat Gain from Equipment assigned with Zone List





Look in the .eio file -- where it will show the expected gains for each zone.

At 07:21 AM 8/30/2011, Jean marais wrote:
My eso output shows a zero heat gain in all zones for

   ! Equipment 1
   ElectricEquipment, AboveGroundZonesNotRoof Equipment 1,  !- Name
      AboveGroundZonesNotRoof,                    !- Zone Name
      On,                                         !- Equipment SCHEDULE Name  ...was..3497
      Watts/Area,                                 !- Design Level calculation method
      ,                                           !- Design Equipment Level (W)
      0.1888,                                     !- Watts per Zone Area {watts/m2} 0.1 x 3079956/201265 = 0.1888
      ,                                           !- Watts per Person {watts/person}
      0,                                          !- Latent fraction
      1,                                          !- Radiant fraction
      0,                                          !- Fraction Lost
      ELECTRIC EQUIPMENT#AllZonesNotRoof#05;  !- End-use category

Is this right? The electric input is reporting as expected, but the heat gain not...ideas?



------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/


__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___