The chillers have a "Sizing Factor" input so that multiple chillers in a plant can be sized correctly when more than 1 chiller is used (e.g., for 3 chillers, sizing factor = 0.333). I don't believe the other HVAC equipment have this same input since you would typically only use 1 system. Check the eio file for the size for inputs specified as autosize. So you are probably right, both system are being sized to meet the entire load. On 8/30/2011 2:39 AM, Jean marais wrote:
-- Richard A. Raustad Senior Research Engineer Florida Solar Energy Center University of Central Florida 1679 Clearlake Road Cocoa, FL 32922-5703 Phone: (321) 638-1454 Fax: (321) 638-1439 or 1010 Visit our web site at: http://www.fsec.ucf.edu UCF - From Promise to Prominence: Celebrating 40 Years __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.