Dear Vinay, Try reporting the airflow and fan power to see if it’s the value you specify or 7x that value. I have not used the zone multiplier, but I’m guessing that it multiplies CFM in the same magnitude as the multiplier, so you now may have a fan at 7 x 7 = 49x. The Building Performance Team From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Vinay Devanathan Hello, I am seeing very high fan power on one of my simulations and hence wanted to check for this issue. Let's say there are 7 typical floors and one zone is created and a Zone Group object is used to replicate the 7 floors using a multiplier. Now in all of those zones, the zone loads will be calculated and multiplied by a factor of 7. So in order to satisfy this zone should we input the designed zone CFM * 7 in the input field for HVAC objects or input just the designed
Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.