Hi, "AvailabilityManagerAssignmentList" in the IO Ref has information on this. You should be able to specify more than one manager of the same type. Suggest you output availability status flag set by each of these individual manager and then the status flag of the air loop to see which manager is acting when. I also believe that they work like "OR" function. Thanks, Chandan On 9/8/2011 7:22 AM, Jim Dirkes wrote:
__._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.