Re: [EnergyPlus_Support] Zone/Floor Multiplier





Yes.  If the HVAC system components are autosized (sizing:zone, sizing:system) then the multiplier will be applied automatically to the autosized values.  For example, if outdoor air requirements are autosized the values in sizing:zone should be for a single instance of the zone.

If the HVAC system components are hard-sized using values in the components, then the sizes must be the multiplied number.  For example, a system supplying 100 cfm to a single instance of Zone1, must supply 700 cfm if Zone1 has a multiplier of 7.

At 11:44 AM 9/8/2011, Vinay Devanathan wrote:


Sure, Linda. Thanks! That will be great.
 
But for now -
 
Is the HVAC system of a zone with multiplier treated the same as described in the Multiplier field description of the Zone object?
 
Thanks much!
 
Vinay

On Thu, Sep 8, 2011 at 1:27 PM, Linda Lawrie <linda@xxxxxxxxxxxxxx> wrote:
 

Looks like it did not get included in the V6 Tips & Tricks document.

Hopefully for V7. If I get the article massaged before release, will put it or send it to you.

At 09:12 AM 9/8/2011, Linda Lawrie wrote:


I cannot at the moment. I do not have access to the docs. Tips is not that big. Just look at the bookmarks. Or maybe it didn t get in v6.



Vinay Devanathan < vinay.devanathan@xxxxxxxxx> wrote:
Linda,
Â
I don't find anything on the Tips and Tricks document. I am not sure why this would be, I cant search for a text "Multiplier", the results return no matching strings.
Â
Could you please give me the page number in the PDF? Sorry for the trouble.
Â
Vinay


On Thu, Sep 8, 2011 at 10:35 AM, Linda Lawrie <linda@xxxxxxxxxxxxxx> wrote:
 
Look at the tips and tricks doc. It has a section on multipliers. If it doesn&apos;t answer the question, tell me.

Vinay Devanathan < vinay.devanathan@xxxxxxxxx> wrote:

Mr. Dirkes,
Â
Thanks for your reply.
Â
I think its the other way round. There is some description on Zone Multipliers under the Zone object in the Multiplier field. It seems like the inputs should be good enough to take care of the mutiplied loads.
Â
Vinay
On Wed, Sep 7, 2011 at 6:22 PM, Jim Dirkes < jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx> wrote:
 
Dear Vinay,
Â
Try reporting the airflow and fan power to see if itâ??s the value you specify or 7x that value.  I have not used the zone multiplier, but Iâ??m guessing that it multiplies CFM in the same magnitude as the multiplier, so you now may have a fan at 7 x 7 = 49x.
Â
The Building Performance Team
James V. Dirkes II, P.E., BEMP , LEED AP
1631 Acacia Drive NW
Grand Rapids, MI 49504
616 450 8653

Â

From: EnergyPlus_Support@xxxxxxxxxxxxxxx [ mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Vinay Devanathan
Sent: Wednesday, September 07, 2011 6:04 PM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: [EnergyPlus_Support] Zone/Floor Multiplier

Â

 

Hello,

Â

I am seeing very high fan power on one of my simulations and hence wanted to check for this issue.

Â

Let's say there are 7 typical floors and one zone is created and a Zone Group object is used to replicate the 7 floors using a multiplier. Now in all of those zones, the zone loads will be calculated and multiplied by a factor of 7. So in order to satisfy this zone should we input the designed zone CFM * 7 in the input field for HVAC objects or input just the designed zone CFM and the software will mutliply it? It would be great if someone can clarify this.

Â

I have it at 7 * designed zone cfm, and hence doubting my approach due to high fan power. At the same time I feel this is the way to do it from vague prior memory.

Â

Thank you in advance.

Â

Vinay

Â










__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___