Re: [EnergyPlus_Support] Suggestion for simple alternative to EnergyPlus EMS custom solution





FYI all -- this is the answer we gave this person from the helpdesk:

EMS is the only system available in EnergyPlus for customizing HVAC controls. Please see the EMS application guide which includes discussion of many examples with increasing levels of complexity.

Right now there is not a way for EMS to look forward in time at future weather file data, so your weather forecast information may be tricky to input and would probably need to be input separately with schedule files.

At 03:19 PM 9/21/2011, Energy Energy wrote:
Looking for a simpler solution to implement a custom heating/cooling strategy in EnergyPlus than through EMS

How would you recommend customizing the HVAC control to allow implementation of a custom heating and cooling strategy.  For example we would like to use the weather forecast and predictive modeling to optimize energy use.


__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___