Hi, you are not only one confused with the OA mixer
operation. There have been many discussion on this topic.
The OA mixer box actually has a splitter in it as well.
The environment is a large air tank. The OA box relief
air node air is feb back to the OA inlet node via the air
tank. The used air becomes the fresh air. The OA inlet
node has a damper.
Because of this air tank connection, the OA relief air
amount is always equal to the OA intake amount, ignoring
the temperature, pressure variation.
The mixer is described in the document. The OA inlet air
is mixed with part of the return air. The output of the
mixer is the mixed air dode.
The splitter is not documented. The input node is the
return air node. The two split paths are the relief air
node and the bypass path to the mixer. I use the name
bypass path, because you all know about the bypass path in
the plant loops. This bypass path bypasses the
environment air tank.
================
1. Are
relief air conditions always equal to the zone return
air conditions for OutdoorAir:Mixer?
A splitter does not change the
temperature, therefore the relief air node temperature
should be the same as the input return air
temperature.
2. How do
you achieve 100% fresh air? If the air flows are
balanced like in the above example does that mean that
flow is 100% outdoor air?
If you want
100% fresh air, the amount of return air through the
bypass path is zero.
"Note
that in the above example flows are balanced. Relief
air kg/s equals outdoor air (.) , mixed air, and
return air kg/s and economiser cycle is off."
This
statement is not very clear. The first condition is
corrent. The rest do not make sense.
3. If the
No. 2 is true why are then mixed air conditions in
1zone evaporative cooler example different from
Outdoor air conditions?
I do not know
your exact air balance conditions. If the (minimum )
air flow of the OA inlet is the same as the return air
flow, all the air will leave through the relief air
node.
======================================
If the OA
inlet flow is zero, all the return air is channel back
to the air loop via the mixed air node. Mixed air
node temperature is the same as the return air
temperature.
If the OA inlet flow rate is the same as the fan flow
rate, 100% fresh air enters through the mixed air node.
However, how do you make the OA inlet flow rate the same
as the fan rate? There is no control to cut off the
bypass path. This is another question. On paper, it is
quite simple. Make the two flow rates equal. In
practice, it is not so simple without defining what you
really meant by 100% fresh air to the zones..
=======================
The four nodes of a zone have the similar configuration.
Two input paths to a mixer into the zone node. The zone
air is split into two outlet paths, exhaust and return air
nodes. The thermostat is connected to the zone, and the
internal load is added to the return node. This is the
way I think of it, and is not the official version.
Dr. Li
To:
EnergyPlus_Support@xxxxxxxxxxxxxxx
From:
dulen@xxxxxxxxxx
Date: Thu, 22 Sep 2011 14:51:09 +1200
Subject: [EnergyPlus_Support] OutdoorAir:Mixer questions
Hi
There,
I
am struggling a bit to understand how
OutdoorAir:Mixer works.
From
reading the i/o manual it appears that
outdoorair:mixer will calculate relief and
mixed air conditions based on mixing of
outdoor air inlet and return from the zone.
If that is the case than the relief air and
mixed air should have the same temperature.
If
you run the 1zone evaporative cooler example
you will notice that that is not the case.
Relief air has the same temperature as
return air from the zone (which makes
sense). That would imply that mixed air
should have same properties as outdoor air
(because air flows are balanced) but again
that is not the case. Mixed air temperature
is higher than outdoor temperature. I would
assume that, because all of the return air
is relieved, there is nothing to mix with
outdoor air?
Note
that in the above example flows are
balanced. Relief air kg/s equals outdoor
air, mixed air, and return air kg/s and
economiser cycle is off.
So
the questions are?
1.
Are relief air conditions always equal to
the zone return air conditions for
OutdoorAir:Mixer?
2.
How do you achieve 100% fresh air? If the
air flows are balanced like in the above
example does that mean that flow is 100%
outdoor air?
3.
If the No. 2 is true why are then mixed air
conditions in 1zone evaporative cooler
example different from Outdoor air
conditions?
Thanks