[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] Real world HVAC question - DCV using CO2 sensors with VAV dampers





Hi,

Have you looked into ASHRAE standard 62.1 user's manual (probably Appendix A). 
I think that talks about something similar to your strategy # 1.

Chandan

On Sat, Sep 24, 2011 at 1:07 PM, James V Dirkes II, PE <jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx> wrote:
 

Dear Jean,

I have some understanding of the origins of CO2 control, which are almost
exclusively based on occupant perception, not health. (Think "body odor"
or "Staleness").

As a result, I do not place a high priority on CO2 control schemes which
use more outdoor air than whatever is needed to maintain about 1000 ppm.
That means I favor something like your Scheme #3, in which the controls
treat the CO2 concentration as a maximum limit.

Keep in mind that any modern control system should not be "erratic"; it
should be able to produce consistent and smooth control of outdoor air to
maintain whatever setpoint you choose.



> This question has nothing to do with simulation as such. What is the best
> way to use / control a Demand Control Ventilation (DCV) System which uses
> a combination of CO2 sensors and motorized Variable Airflow Volume (VAV)
> dampers.
>
> I will suggest a control stradegy to illustrate the question:
>
> CO2 sensors report the zone CO2 level at given timestep.
> Allowable upperbound CO2 level is 800ppm.
> Outdoor Air (ODA) CO2 level is 400ppm.
> Minimum damper position allows at least 0.3 of fully open flow.
> Maximum damper position is fully open, i.e. 1.0 of full flow.
>
> Stradegy 1::
> Control is such that at 400 ppm, Damper will be at 0.3 of full flow.
> At 800 ppm or more, Damper will be fully open.
> Damper is linierly actuated between 0.3 to 1 as the level of zone CO2
> increases from 400 ppm to 800 ppm.
>
> Stradegy 2::
> Damper remains at 0.3 untill CO2 level reaches 750 ppm, then linierly
> opens from 0.3 to 1.0 as the level increases to 800 ppm.
>
> Stradegy 3::
> Erratic opening and closing of damper only when level reaches or goes over
> 800 ppm.
>
> Stradegy 4::
> Exponencial, or other curve to control damper other than liniear.
>
> Origional question...how are these systems controlled in practice?
> Anyone with experience, here?
>
>




__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___