[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

RE: [EnergyPlus_Support] Re: OutdoorAir:Mixer questions



Dr. Li,

Apparently I dopped into the middle of the conversation without reading
the previous discussion  Sorry!

I was only addressing the issue of modeling infiltration.

>
> Hi, Jim What I was suggesting was not to over simulate. Many user had
> asked "how to simulate 100% fresh air intake?"  and "How to feed a wanted
> amount of fresh air to each zone with a dual system? As we are not really
> accounting for every crack in the building, how a zone is dividing the air
> through the exhaust and return path,  I am suggesting that all the air
> comes from this environment air tank and return to this air tank. With the
> mixer and spliter idea, temperature will change at the mixer output node
> and not at the splitter branches.  This is where all these discussion
> started.  Why the mixed air node temperature does not change, or follow
> the OA temperature. The actual problem was not in the OA mixer.  The air
> loop was not used to cool and heat the zone, therefore the strange
> results.
>
>  Dr. Li
>  To: EnergyPlus_Support@xxxxxxxxxxxxxxx
> From: jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx
> Date: Sat, 24 Sep 2011 12:59:04 -0400
> Subject: RE: [EnergyPlus_Support] Re: OutdoorAir:Mixer questions
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>       Dear Jean,
>
>
>
> As you and Dr. Li indicate, the air balance of a real building is very
>
> complex.  The fact that real air zones can exchange air in a multitude of
>
> ways, and that actual "crack area" is impossible to quantify without
>
> extensive physical testing, means that our efforts to model them are
>
> doomed as far as any correlation between real life and the model goes.
>
>
>
> For those reasons, I don't expect to have high accuracy regarding
>
> infiltration.  Rather, I try to prepare the model so that it's defensible
>
> to another knowledgeable person and (hopefully) keep the warnings at a low
>
> level.
>
>
>
> The @#$%^& imbalanced airflow warning is an annoyance, especially when you
>
> get a few million of them, as I am prone to do. I've recently begun trying
>
> to improve my input process so as to minimize these warnings.  Next steps
>
> include understanding the ZoneMixing object better (as suggested by Dr.
>
> Li), since it may help.  Keep in mind that this is only to reduce the
>
> number of warnings; I doubt that any accuracy improvement will be
>
> provable.
>
>
>
>>
>
>>
>
>> Hi, Jean If the kitchen air is exhausted to the enveronment air tank,
>> the
>
>> kitchen zone return air is reduced, therefore there will be less air for
>
>> the OA mixer  relief node.  This is another interesting point.  All the
>> OA
>
>> mixer,  infiltration and ventelation paths are also through mixer and
>
>> splitter pair in the OA tank. With AFN, the pressure change (wind
>
>> velosity)  is added to the tank. If the exhaust air is larger than the
>> OA
>
>> inlet, the air must come from the leaks.   In practice, you will hear
>> the
>
>> speed of the exhaust fan chaning, as you open and close the kitchen
>> door.
>
>> Un-balanced air between zone is handled by zone mixing, or plenum. That
>
>> was the reason why I said you can say 100% fresh air from OA by making
>
>> inlet flow rate the same as the fan rate.  In practice, it is not easy
>> to
>
>> do.  You can specify min. rate of OA equals to max flow rate of the fan.
>
>> The return air amount is not known or specified, and the zone exhaust
>> and
>
>> inlet can be from other paths of the OA tank.   Dr. Li
>
>>  To: EnergyPlus_Support@xxxxxxxxxxxxxxx
>
>> From: jeannieboef@xxxxxxxxx
>
>> Date: Sat, 24 Sep 2011 11:53:04 +0000
>
>> Subject: [EnergyPlus_Support] Re: OutdoorAir:Mixer questions
>
>>
>
>>
>
>>
>
>>
>
>>
>
>>
>
>>
>
>>
>
>>
>
>>
>
>>
>
>>
>
>>
>
>>
>
>>
>
>>
>
>>
>
>>
>
>>
>
>>
>
>>
>
>>
>
>>
>
>>
>
>>
>
>>
>
>>
>
>>
>
>>       Hi Dr. Li,
>
>>
>
>> I find the "environment tank" analogy very interesting. Particularly,
>> that
>
>> the relief air is equal to the ODA flowing into the ODA system. In real
>
>> life as in the simulation more than 1 system may be present, e.g. AHU
>
>> serves supply air to both office and kitchen zones, but the kitchen has
>
>> it's own fan:zoneexhaust to the outdoors.
>
>>
>
>>
>
>>
>
>> In this case the relief air of the AHU is not equal to the supply air,
>> but
>
>> the "environment tank" remains balanced as the kitchen also exhausts to
>
>> it.
>
>>
>
>>
>
>>
>
>> Now when kitchen makeup air is the combination of supply air and
>
>> infiltrated via the office zones, it becomes tricky. As the demands of
>> the
>
>> kitchen and the offices are independant, it may occure that the flow is
>
>> unbalanced at any possible timepoint. Should one not wish to use an AFN
>
>> crack between kitchen and office and office and outdoors, is there a way
>
>> you would suggest to address the unbalanced flow?
>
>>
>
>>
>
>>
>
>> e+ simply issues the warning that the unbalanced air is not flowing in
>
>> from outdoors and may decrease the accuracy of results.
>
>>
>
>>
>
>>
>
>>
>
>>
>
>>
>
>>
>
>>
>
>>
>
>>
>
>>
>
>>
>
>>
>
>>
>
>>
>
>>
>
>>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>




------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to: