Richard, May we know pg 12 of which document? A search using 'SCOP'
and 'Coefficient of Performance' in index of the E+Documentation did
not reveal anything you stated. Thanks. ooi
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Richard Raustad
<RRaustad@...> wrote:
Look at the definition for seasonal coefficient of performance -
heating
(SCOPh) on pg 12.
The SCOP and COP do not mean the same thing. You need to use the
rated
COP and capacity of the equipment in your simulation.
On 9/28/2011 11:42 AM, Jiju Kin wrote:
>
> Hi,
>
> I am doing simulation for LEED certification and not understand
how if
> determines the SCOP in Table 6.8.1A (ASHRAE 90.1 2007), is the
same as
> COP? the simulation options exists only the COP as a parameter to
be
> used.
>
> JijuKin
>
--
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL 32922-5703
Phone: (321) 638-1454
Fax: (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu
UCF - From Promise to Prominence: Celebrating 40 Years
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to
energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone
has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under
the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/