|
If you are an advanced EPlus user, go ahead and try it.
Otherwise, using a thermostat to control a HVAC in the next room with a open door partition, is just the same as a single zone with the theremostat mounted away from the fan coil unit. EPlus does not specify the location of the theremostat and the HVAC unit in a zone. Dr. Li To: EnergyPlus_Support@xxxxxxxxxxxxxxx From: laxoayi@xxxxxxxxxxxxxxxx Date: Sat, 1 Oct 2011 18:37:45 +0000 Subject: [EnergyPlus_Support] Re: Availability of IdealLoadsAirSystem using EMS
Thanks for your reply.
I'll describe what I'm trying to achieve and hopefully you can advise. Consider I have two adjacent thermal zones A and B connected by an opening using AFN objects. Zone A is controlled using an IdealLoadsAirSystem with a thermostat control type always as ThermostatSetpoint:SingleHeatingorCooling (i.e. the IdealLoadsAirSystem is always on) and a setpoint schedule specified for the same zone. Zone B on the other hand is uncontrolled. Is it possible to use EMS to control the availability (i.e. turning on/off) of the IdealLoadsAirSystem in zone A using the mean air temperature in Zone B. I believe that in this case the EMS sensor will be zone B's mean air temperature but I can't figure out what the actuator for the IdealLoadsAirSystem is. Any Ideas? Thanks in advance, your help is very much appreciated. --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, YuanLu Li <yli006@...> wrote: > > > IdealLoadsAirSystem is individual zone thermostat controlled. You may have used a common setpoint schedule, and a common type declaration for the thermostat.. > Each zone is turned off when the zone mean temperature has reached the scheduled set point temperature. The dual-band dead band can be adjusted to disable the system completely, zone by zone. Dr. Li > To: EnergyPlus_Support@xxxxxxxxxxxxxxx > From: laxoayi@... > Date: Thu, 29 Sep 2011 11:22:13 +0000 > Subject: [EnergyPlus_Support] Availability of IdealLoadsAirSystem using EMS > > > > > > > > > > > > > > > > > > > > > > > > > > > > > Hi All, > > Is it possible to use EMS to control the availabilty of an Ideal Loads Air System depending on the zone's mean air temperature as a sensor? > > Thanks, > > Omar > __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |