RE: [EnergyPlus_Support] Re: Availability of IdealLoadsAirSystem using EMS





If you are an advanced EPlus user, go ahead and try it.
 
Otherwise, using a thermostat to control a HVAC in the next room with a open door partition, is just the same as a single zone with the theremostat mounted away from the fan coil unit.
 
EPlus does not specify the location of the theremostat and the HVAC unit in a zone.

 Dr. Li  

 

To: EnergyPlus_Support@xxxxxxxxxxxxxxx
From: laxoayi@xxxxxxxxxxxxxxxx
Date: Sat, 1 Oct 2011 18:37:45 +0000
Subject: [EnergyPlus_Support] Re: Availability of IdealLoadsAirSystem using EMS

 
Thanks for your reply.
I'll describe what I'm trying to achieve and hopefully you can advise. Consider I have two adjacent thermal zones A and B connected by an opening using AFN objects. Zone A is controlled using an IdealLoadsAirSystem with a thermostat control type always as ThermostatSetpoint:SingleHeatingorCooling (i.e. the IdealLoadsAirSystem is always on) and a setpoint schedule specified for the same zone. Zone B on the other hand is uncontrolled.
Is it possible to use EMS to control the availability (i.e. turning on/off) of the IdealLoadsAirSystem in zone A using the mean air temperature in Zone B. I believe that in this case the EMS sensor will be zone B's mean air temperature but I can't figure out what the actuator for the IdealLoadsAirSystem is. Any Ideas?

Thanks in advance, your help is very much appreciated.

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, YuanLu Li <yli006@...> wrote:
>
>
> IdealLoadsAirSystem is individual zone thermostat controlled. You may have used a common setpoint schedule, and a common type declaration for the thermostat..
> Each zone is turned off when the zone mean temperature has reached the scheduled set point temperature. The dual-band dead band can be adjusted to disable the system completely, zone by zone. Dr. Li
> To: EnergyPlus_Support@xxxxxxxxxxxxxxx
> From: laxoayi@...
> Date: Thu, 29 Sep 2011 11:22:13 +0000
> Subject: [EnergyPlus_Support] Availability of IdealLoadsAirSystem using EMS
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
> Hi All,
>
> Is it possible to use EMS to control the availabilty of an Ideal Loads Air System depending on the zone's mean air temperature as a sensor?
>
> Thanks,
>
> Omar
>




__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___