[EnergyPlus_Support] Re: Help me to create the VAV system and zone
Okey, so for exemple, the first "severe" is :
** Severe ** Node Connection Error, Node="BLOCK1:MEETINGROOM REHEAT COIL HW INLET", Inlet node did not find an appropriate matching "outlet" node.
** ~~~ ** If this is an outdoor air inlet node, it must be listed in an OutdoorAir:Node or OutdoorAir:NodeList object.
** ~~~ ** Reference Object=BRANCH, Name=BLOCK1:MEETINGROOM REHEAT COIL HW BRANCH
And the EXPIDF give me this :
But I don't see any probleme, input-->input,output-->output for the water. But for the Air ....
Coil:Heating:Water,
Block1:Meetingroom Reheat Coil, !- Name
HVACTemplate-Always 1, !- Availability Schedule Name
autosize, !- UA of the Coil {W/K}
autosize, !- Max Water Flow Rate of Coil {m3/s}
Block1:Meetingroom Reheat Coil HW Inlet, !- Coil Water Inlet Node
Block1:Meetingroom Reheat Coil HW Outlet, !- Coil Water Outlet Node
Block1:Meetingroom Damper Outlet, !- Air Inlet Node Name
Block1:Meetingroom Supply Inlet, !- Air Outlet Node Name
UFactorTimesAreaAndDesignWaterFlowRate, !- Performance Input Method
autosize, !- Rated Capacity
82.2, !- Rated Inlet Water Temperature
16.6, !- Rated Inlet Air Temperature
71.1, !- Rated Outlet Water Temperature
32.2, !- Rated Outlet Air Temperature
1.0; !- Rated Ratio for Air and Water Convection
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/