[EnergyPlus_Support] Re: Help me to create the VAV system and zone



I don't have Plant... I thought the System Template contains all I need except the zone area and the thermostat.

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Richard Raustad <RRaustad@...> wrote:
>
> You don't have an HVACTemplate:Plant:* do you......look at the example 
> file HVACTemplate-5ZoneVAVFanPowered.idf
> 
> On 10/14/2011 9:20 AM, xav31sob wrote:
> >
> > Okey, so for exemple, the first "severe" is :
> >
> > ** Severe ** Node Connection Error, Node="BLOCK1:MEETINGROOM REHEAT 
> > COIL HW
> > INLET", Inlet node did not find an appropriate matching "outlet" node.
> > ** ~~~ ** If this is an outdoor air inlet node, it must be listed in an
> > OutdoorAir:Node or OutdoorAir:NodeList object.
> > ** ~~~ ** Reference Object=BRANCH, Name=BLOCK1:MEETINGROOM REHEAT COIL HW
> > BRANCH
> >
> > And the EXPIDF give me this :
> > But I don't see any probleme, input-->input,output-->output for the 
> > water....
> >
> > Branch,
> > Block1:Meetingroom Reheat Coil HW Branch, !- Name
> > , !- Maximum Branch Flow Rate {m3/s}
> > , !- Pressure Drop Curve Name
> > Coil:Heating:Water, !- Component 1 Object Type
> > Block1:Meetingroom Reheat Coil, !- Component 1 Name
> > Block1:Meetingroom Reheat Coil HW Inlet, !- Component 1 Inlet Node Name
> > Block1:Meetingroom Reheat Coil HW Outlet, !- Component 1 Outlet Node Name
> > Active;
> >
> > 
> 
> -- 
> Richard A. Raustad
> Senior Research Engineer
> Florida Solar Energy Center
> University of Central Florida
> 1679 Clearlake Road
> Cocoa, FL  32922-5703
> Phone:   (321) 638-1454
> Fax:     (321) 638-1439 or 1010
> Visit our web site at: http://www.fsec.ucf.edu
> 
> UCF - From Promise to Prominence: Celebrating 40 Years
>




------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/