Re: [EnergyPlus_Support] Re: Help me to create the VAV system and zone





HVACTemplate:System means the air system, the HVACTemplate:Plant takes care of the water side.

On 10/14/2011 9:41 AM, xav31sob wrote:
 

I don't have Plant... I thought the System Template contains all I need except the zone area and the thermostat.

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Richard Raustad <RRaustad@...> wrote:
>
> You don't have an HVACTemplate:Plant:* do you......look at the example
> file HVACTemplate-5ZoneVAVFanPowered.idf
>
> On 10/14/2011 9:20 AM, xav31sob wrote:
> >
> > Okey, so for exemple, the first "severe" is :
> >
> > ** Severe ** Node Connection Error, Node="BLOCK1:MEETINGROOM REHEAT
> > COIL HW
> > INLET", Inlet node did not find an appropriate matching "outlet" node.
> > ** ~~~ ** If this is an outdoor air inlet node, it must be listed in an
> > OutdoorAir:Node or OutdoorAir:NodeList object.
> > ** ~~~ ** Reference Object=BRANCH, Name=BLOCK1:MEETINGROOM REHEAT COIL HW
> > BRANCH
> >
> > And the EXPIDF give me this :
> > But I don't see any probleme, input-->input,output-->output for the
> > water....
> >
> > Branch,
> > Block1:Meetingroom Reheat Coil HW Branch, !- Name
> > , !- Maximum Branch Flow Rate {m3/s}
> > , !- Pressure Drop Curve Name
> > Coil:Heating:Water, !- Component 1 Object Type
> > Block1:Meetingroom Reheat Coil, !- Component 1 Name
> > Block1:Meetingroom Reheat Coil HW Inlet, !- Component 1 Inlet Node Name
> > Block1:Meetingroom Reheat Coil HW Outlet, !- Component 1 Outlet Node Name
> > Active;
> >
> >
>
> --
> Richard A. Raustad
> Senior Research Engineer
> Florida Solar Energy Center
> University of Central Florida
> 1679 Clearlake Road
> Cocoa, FL 32922-5703
> Phone: (321) 638-1454
> Fax: (321) 638-1439 or 1010
> Visit our web site at: http://www.fsec.ucf.edu
>
> UCF - From Promise to Prominence: Celebrating 40 Years
>


-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years


__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___