I try to find this example, and I fixe the problem.
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Richard Raustad <RRaustad@...> wrote:
>
> HVACTemplate:System means the air system, the HVACTemplate:Plant takes 
> care of the water side.
> 
> On 10/14/2011 9:41 AM, xav31sob wrote:
> >
> > I don't have Plant... I thought the System Template contains all I 
> > need except the zone area and the thermostat.
> >
> > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx 
> > <mailto:EnergyPlus_Support%40yahoogroups.com>, Richard Raustad 
> > <RRaustad@> wrote:
> > >
> > > You don't have an HVACTemplate:Plant:* do you......look at the example
> > > file HVACTemplate-5ZoneVAVFanPowered.idf
> > >
> > > On 10/14/2011 9:20 AM, xav31sob wrote:
> > > >
> > > > Okey, so for exemple, the first "severe" is :
> > > >
> > > > ** Severe ** Node Connection Error, Node="BLOCK1:MEETINGROOM REHEAT
> > > > COIL HW
> > > > INLET", Inlet node did not find an appropriate matching "outlet" node.
> > > > ** ~~~ ** If this is an outdoor air inlet node, it must be listed 
> > in an
> > > > OutdoorAir:Node or OutdoorAir:NodeList object.
> > > > ** ~~~ ** Reference Object=BRANCH, Name=BLOCK1:MEETINGROOM REHEAT 
> > COIL HW
> > > > BRANCH
> > > >
> > > > And the EXPIDF give me this :
> > > > But I don't see any probleme, input-->input,output-->output for the
> > > > water....
> > > >
> > > > Branch,
> > > > Block1:Meetingroom Reheat Coil HW Branch, !- Name
> > > > , !- Maximum Branch Flow Rate {m3/s}
> > > > , !- Pressure Drop Curve Name
> > > > Coil:Heating:Water, !- Component 1 Object Type
> > > > Block1:Meetingroom Reheat Coil, !- Component 1 Name
> > > > Block1:Meetingroom Reheat Coil HW Inlet, !- Component 1 Inlet Node 
> > Name
> > > > Block1:Meetingroom Reheat Coil HW Outlet, !- Component 1 Outlet 
> > Node Name
> > > > Active;
> > > >
> > > >
> > >
> > > --
> > > Richard A. Raustad
> > > Senior Research Engineer
> > > Florida Solar Energy Center
> > > University of Central Florida
> > > 1679 Clearlake Road
> > > Cocoa, FL 32922-5703
> > > Phone: (321) 638-1454
> > > Fax: (321) 638-1439 or 1010
> > > Visit our web site at: http://www.fsec.ucf.edu
> > >
> > > UCF - From Promise to Prominence: Celebrating 40 Years
> > >
> >
> > 
> 
> -- 
> Richard A. Raustad
> Senior Research Engineer
> Florida Solar Energy Center
> University of Central Florida
> 1679 Clearlake Road
> Cocoa, FL  32922-5703
> Phone:   (321) 638-1454
> Fax:     (321) 638-1439 or 1010
> Visit our web site at: http://www.fsec.ucf.edu
> 
> UCF - From Promise to Prominence: Celebrating 40 Years
>




------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/