[EnergyPlus_Support] Re: Modelling Vents in naturally ventilated buildings





Juaneco_2710,

I would go for the AirFlow Network model. See Group - Airflow Network in the Input/Output documentation.
I find "CIBSE AM10 - Natural ventilation in non-domestic buildings", a good reference for natural ventilation, common value used for discharge coefficients is 0.61, but this would imply you have the effective area opening of the vents (from manufacturer).  For estimation of wind pressure coefficients you can refer to CIBSE AM10 as well.
Also, if you can use Design Builder, this has a feature do automatically place vents, it will assume some of this values, and wind pressure coefficients are based on the following document.  http://www.designbuilder.co.uk/downloadsv1/AIVCWindPressureCoefficientData.pdf
 




--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "juaneco_2710" <juaneco_2710@...> wrote:
>
> I am trying to model a small office building in Bogotá, Colombia. It uses natural ventilation as cooling mechanism. To increase the airflow, architects added vents above all windows. I woud like to know what is the correct way to model these vents: what kind of object to create, what are the correct coefficients (e.g. discharge coefficient) and so on.
> 
> Thanks.
>




------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/