I do not know what is in :-
System Fan Power according (ASHRAE 90.1-2007, appendix G) . Change your pressure rise input to 'autosize', if this is an allowed option, and see what fan power is needed. If this does not work, the problem is not in the fan power. Dr. Li To: EnergyPlus_Support@xxxxxxxxxxxxxxx From: alvaro.urrutia@xxxxxxxxx Date: Tue, 18 Oct 2011 06:14:14 -0700 Subject: Re: [EnergyPlus_Support] Re: Severe errors for Fan Power modeling of VAV system
Thanks a lot for every answer.
James in bldg-sim mailing list post proposes a method for incorporate System Fan Power in Energyplus simulation modifing Supply Fan Delta Pressure (for my model is 1495Pa), but when I apply this pressure settings, simulation shows all this errors. I apreciate if anyone could me explain more detailly some procedure for model System Fan Power according (ASHRAE 90.1-2007, appendix G) in energyplus model. From: Jim Dirkes <jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx> To: EnergyPlus_Support@xxxxxxxxxxxxxxx Sent: Tuesday, October 18, 2011 7:30 AM Subject: RE: [EnergyPlus_Support] Re: Severe errors for Fan Power modeling of VAV system Also, Once I mistakenly had a zero in the place of a proper setpoint on the Winter DesignDay. One number among thousands! The Building Performance Team
From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Jean marais
I bet the coil setpoints are too low because the coils are auto sized and the user specified airflow is too little to achieve the needed cooling with a normal coil working at setpoints between 12 and 18 deg C. The program is trying to cool very little air very cold to bring enough "cold energy" into the room. __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |