[EnergyPlus_Support] Re: HVAC Template : Zone and Plant, Should I connect the nodes ?
The main errors :
** Warning ** Could not find Coil:Heating:Water with name BLOCK1:MEETINGROOM HEATING COIL on any plant loop
** ~~~ ** Autosizing of water flow requires a heating loop Sizing:Plant object
** ~~~ ** Occurs in ZoneHVAC:FourPipeFanCoil Object=BLOCK1:MEETINGROOM FAN COIL
** Warning ** Could not find COIL:COOLING:WATER with name BLOCK1:MEETINGROOM COOLING COIL on any plant loop
** ~~~ ** Autosizing of water flow requires a cooling loop Sizing:Plant object
** ~~~ ** Occurs in ZoneHVAC:FourPipeFanCoil Object=BLOCK1:MEETINGROOM FAN COIL
** Fatal ** Preceeding sizing errors cause program termination
...Summary of Errors that led to program termination:
..... Reference severe error count=2
..... Last severe error=FenestrationSurface:Detailed="BLOCK1:MEETINGROOM_PARTITION_5_0_0_0_0_0_WIN", invalid Building Surface Name="BLOCK1:MEETINGROOM_PARTITION_5_0_0".
************* Fatal error -- final processing. More error messages may appear.
************* Testing Individual Branch Integrity
** Warning ** There are orphaned Branches in input
************* All Branches passed integrity testing
************* Testing Individual Supply Air Path Integrity
************* All Supply Air Paths passed integrity testing
************* Testing Individual Return Air Path Integrity
************* All Return Air Paths passed integrity testing
** Severe ** Node Connection Error, Node="BLOCK1:MEETINGROOM COOLING COIL CHW INLET", Inlet node did not find an appropriate matching "outlet" node.
** ~~~ ** If this is an outdoor air inlet node, it must be listed in an OutdoorAir:Node or OutdoorAir:NodeList object.
** ~~~ ** Reference Object=BRANCH, Name=BLOCK1:MEETINGROOM COOLING COIL CHW BRANCH
** Severe ** Node Connection Error, Node="BLOCK1:MEETINGROOM HEATING COIL HW INLET", Inlet node did not find an appropriate matching "outlet" node.
** ~~~ ** If this is an outdoor air inlet node, it must be listed in an OutdoorAir:Node or OutdoorAir:NodeList object.
** ~~~ ** Reference Object=BRANCH, Name=BLOCK1:MEETINGROOM HEATING COIL HW BRANCH
** Severe ** Node Connection Error, Node="BLOCK1:MEETINGROOM HEATING COIL HW INLET", Inlet node did not find an appropriate matching "outlet" node.
** ~~~ ** If this is an outdoor air inlet node, it must be listed in an OutdoorAir:Node or OutdoorAir:NodeList object.
** ~~~ ** Reference Object=COIL:HEATING:WATER, Name=BLOCK1:MEETINGROOM HEATING COIL
** Severe ** Node Connection Error, Node="BLOCK1:MEETINGROOM COOLING COIL CHW INLET", Inlet node did not find an appropriate matching "outlet" node.
** ~~~ ** If this is an outdoor air inlet node, it must be listed in an OutdoorAir:Node or OutdoorAir:NodeList object.
** ~~~ ** Reference Object=COIL:COOLING:WATER, Name=BLOCK1:MEETINGROOM COOLING COIL
** Severe ** Node Connection Error, Node="BLOCK1:MEETINGROOM MIXED AIR OUTLET", Inlet node did not find an appropriate matching "outlet" node.
** ~~~ ** If this is an outdoor air inlet node, it must be listed in an OutdoorAir:Node or OutdoorAir:NodeList object.
** ~~~ ** Reference Object=FAN:CONSTANTVOLUME, Name=BLOCK1:MEETINGROOM SUPPLY FAN
** Warning ** Node Connection errors shown during "fatal error" processing may be false because not all inputs may have been retrieved.
** Warning ** Node Connection Error for object UNDEFINED, name=BLOCK1:MEETINGROOM OA MIXING BOX
** ~~~ ** UNDEFINED not on any Branch or Parent Object
** ~~~ ** Inlet Node : BLOCK1:MEETINGROOM OUTSIDE AIR INLET
** ~~~ ** Outlet Node: UNDEFINED
** Warning ** Potential Node Connection Error for object UNDEFINED, name=BLOCK1:MEETINGROOM OA MIXING BOX
** ~~~ ** Node Types are still UNDEFINED -- See Branch/Node Details file for further information
** ~~~ ** Inlet Node : BLOCK1:MEETINGROOM OUTSIDE AIR INLET
** ~~~ ** Outlet Node: UNDEFINED
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/