[EnergyPlus_Support] Re: HVAC Template : Zone and Plant, Should I connect the nodes ?



It seem to be a problem with the Fancoil template. I don't undestand why but the OA Mixing Box don't have any output ... I think it's my main problem, but why ?

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "xav31sob" <rockcolomiers@...> wrote:
>
> The main errors : 
> 
>    ** Warning ** Could not find Coil:Heating:Water with name BLOCK1:MEETINGROOM HEATING COIL on any plant loop
>    **   ~~~   ** Autosizing of water flow requires a heating loop Sizing:Plant object
>    **   ~~~   ** Occurs in ZoneHVAC:FourPipeFanCoil Object=BLOCK1:MEETINGROOM FAN COIL
>    ** Warning ** Could not find COIL:COOLING:WATER with name BLOCK1:MEETINGROOM COOLING COIL on any plant loop
>    **   ~~~   ** Autosizing of water flow requires a cooling loop Sizing:Plant object
>    **   ~~~   ** Occurs in ZoneHVAC:FourPipeFanCoil Object=BLOCK1:MEETINGROOM FAN COIL
>    **  Fatal  ** Preceeding sizing errors cause program termination
>    ...Summary of Errors that led to program termination:
>    ..... Reference severe error count=2
>    ..... Last severe error=FenestrationSurface:Detailed="BLOCK1:MEETINGROOM_PARTITION_5_0_0_0_0_0_WIN", invalid Building Surface Name="BLOCK1:MEETINGROOM_PARTITION_5_0_0".
>    ************* Fatal error -- final processing.  More error messages may appear.
>    ************* Testing Individual Branch Integrity
>    ** Warning ** There are orphaned Branches in input
>    ************* All Branches passed integrity testing
>    ************* Testing Individual Supply Air Path Integrity
>    ************* All Supply Air Paths passed integrity testing
>    ************* Testing Individual Return Air Path Integrity
>    ************* All Return Air Paths passed integrity testing
>    ** Severe  ** Node Connection Error, Node="BLOCK1:MEETINGROOM COOLING COIL CHW INLET", Inlet node did not find an appropriate matching "outlet" node.
>    **   ~~~   ** If this is an outdoor air inlet node, it must be listed in an OutdoorAir:Node or OutdoorAir:NodeList object.
>    **   ~~~   ** Reference Object=BRANCH, Name=BLOCK1:MEETINGROOM COOLING COIL CHW BRANCH
>    ** Severe  ** Node Connection Error, Node="BLOCK1:MEETINGROOM HEATING COIL HW INLET", Inlet node did not find an appropriate matching "outlet" node.
>    **   ~~~   ** If this is an outdoor air inlet node, it must be listed in an OutdoorAir:Node or OutdoorAir:NodeList object.
>    **   ~~~   ** Reference Object=BRANCH, Name=BLOCK1:MEETINGROOM HEATING COIL HW BRANCH
>    ** Severe  ** Node Connection Error, Node="BLOCK1:MEETINGROOM HEATING COIL HW INLET", Inlet node did not find an appropriate matching "outlet" node.
>    **   ~~~   ** If this is an outdoor air inlet node, it must be listed in an OutdoorAir:Node or OutdoorAir:NodeList object.
>    **   ~~~   ** Reference Object=COIL:HEATING:WATER, Name=BLOCK1:MEETINGROOM HEATING COIL
>    ** Severe  ** Node Connection Error, Node="BLOCK1:MEETINGROOM COOLING COIL CHW INLET", Inlet node did not find an appropriate matching "outlet" node.
>    **   ~~~   ** If this is an outdoor air inlet node, it must be listed in an OutdoorAir:Node or OutdoorAir:NodeList object.
>    **   ~~~   ** Reference Object=COIL:COOLING:WATER, Name=BLOCK1:MEETINGROOM COOLING COIL
>    ** Severe  ** Node Connection Error, Node="BLOCK1:MEETINGROOM MIXED AIR OUTLET", Inlet node did not find an appropriate matching "outlet" node.
>    **   ~~~   ** If this is an outdoor air inlet node, it must be listed in an OutdoorAir:Node or OutdoorAir:NodeList object.
>    **   ~~~   ** Reference Object=FAN:CONSTANTVOLUME, Name=BLOCK1:MEETINGROOM SUPPLY FAN
>    ** Warning ** Node Connection errors shown during "fatal error" processing may be false because not all inputs may have been retrieved.
>    ** Warning ** Node Connection Error for object UNDEFINED, name=BLOCK1:MEETINGROOM OA MIXING BOX
>    **   ~~~   **   UNDEFINED not on any Branch or Parent Object
>    **   ~~~   **   Inlet Node : BLOCK1:MEETINGROOM OUTSIDE AIR INLET
>    **   ~~~   **   Outlet Node: UNDEFINED
>    ** Warning ** Potential Node Connection Error for object UNDEFINED, name=BLOCK1:MEETINGROOM OA MIXING BOX
>    **   ~~~   **   Node Types are still UNDEFINED -- See Branch/Node Details file for further information
>    **   ~~~   **   Inlet Node : BLOCK1:MEETINGROOM OUTSIDE AIR INLET
>    **   ~~~   **   Outlet Node: UNDEFINED
>




------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/