Why don't you look at the example file HVACTemplate-5ZoneFanCoil.idf and see what HVACTemplate objects are used and how they are related.

On 10/19/2011 6:32 AM, xav31sob wrote:
 

It seem to be a problem with the Fancoil template. I don't undestand why but the OA Mixing Box don't have any output ... I think it's my main problem, but why ?

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "xav31sob" <rockcolomiers@...> wrote:
>
> The main errors :
>
> ** Warning ** Could not find Coil:Heating:Water with name BLOCK1:MEETINGROOM HEATING COIL on any plant loop
> ** ~~~ ** Autosizing of water flow requires a heating loop Sizing:Plant object
> ** ~~~ ** Occurs in ZoneHVAC:FourPipeFanCoil Object=BLOCK1:MEETINGROOM FAN COIL
> ** Warning ** Could not find COIL:COOLING:WATER with name BLOCK1:MEETINGROOM COOLING COIL on any plant loop
> ** ~~~ ** Autosizing of water flow requires a cooling loop Sizing:Plant object
> ** ~~~ ** Occurs in ZoneHVAC:FourPipeFanCoil Object=BLOCK1:MEETINGROOM FAN COIL
> ** Fatal ** Preceeding sizing errors cause program termination
> ...Summary of Errors that led to program termination:
> ..... Reference severe error count=2
> ..... Last severe error=FenestrationSurface:Detailed="BLOCK1:MEETINGROOM_PARTITION_5_0_0_0_0_0_WIN", invalid Building Surface Name="BLOCK1:MEETINGROOM_PARTITION_5_0_0".
> ************* Fatal error -- final processing. More error messages may appear.
> ************* Testing Individual Branch Integrity
> ** Warning ** There are orphaned Branches in input
> ************* All Branches passed integrity testing
> ************* Testing Individual Supply Air Path Integrity
> ************* All Supply Air Paths passed integrity testing
> ************* Testing Individual Return Air Path Integrity
> ************* All Return Air Paths passed integrity testing
> ** Severe ** Node Connection Error, Node="BLOCK1:MEETINGROOM COOLING COIL CHW INLET", Inlet node did not find an appropriate matching "outlet" node.
> ** ~~~ ** If this is an outdoor air inlet node, it must be listed in an OutdoorAir:Node or OutdoorAir:NodeList object.
> ** ~~~ ** Reference Object=BRANCH, Name=BLOCK1:MEETINGROOM COOLING COIL CHW BRANCH
> ** Severe ** Node Connection Error, Node="BLOCK1:MEETINGROOM HEATING COIL HW INLET", Inlet node did not find an appropriate matching "outlet" node.
> ** ~~~ ** If this is an outdoor air inlet node, it must be listed in an OutdoorAir:Node or OutdoorAir:NodeList object.
> ** ~~~ ** Reference Object=BRANCH, Name=BLOCK1:MEETINGROOM HEATING COIL HW BRANCH
> ** Severe ** Node Connection Error, Node="BLOCK1:MEETINGROOM HEATING COIL HW INLET", Inlet node did not find an appropriate matching "outlet" node.
> ** ~~~ ** If this is an outdoor air inlet node, it must be listed in an OutdoorAir:Node or OutdoorAir:NodeList object.
> ** ~~~ ** Reference Object=COIL:HEATING:WATER, Name=BLOCK1:MEETINGROOM HEATING COIL
> ** Severe ** Node Connection Error, Node="BLOCK1:MEETINGROOM COOLING COIL CHW INLET", Inlet node did not find an appropriate matching "outlet" node.
> ** ~~~ ** If this is an outdoor air inlet node, it must be listed in an OutdoorAir:Node or OutdoorAir:NodeList object.
> ** ~~~ ** Reference Object=COIL:COOLING:WATER, Name=BLOCK1:MEETINGROOM COOLING COIL
> ** Severe ** Node Connection Error, Node="BLOCK1:MEETINGROOM MIXED AIR OUTLET", Inlet node did not find an appropriate matching "outlet" node.
> ** ~~~ ** If this is an outdoor air inlet node, it must be listed in an OutdoorAir:Node or OutdoorAir:NodeList object.
> ** ~~~ ** Reference Object=FAN:CONSTANTVOLUME, Name=BLOCK1:MEETINGROOM SUPPLY FAN
> ** Warning ** Node Connection errors shown during "fatal error" processing may be false because not all inputs may have been retrieved.
> ** Warning ** Node Connection Error for object UNDEFINED, name=BLOCK1:MEETINGROOM OA MIXING BOX
> ** ~~~ ** UNDEFINED not on any Branch or Parent Object
> ** ~~~ ** Inlet Node : BLOCK1:MEETINGROOM OUTSIDE AIR INLET
> ** ~~~ ** Outlet Node: UNDEFINED
> ** Warning ** Potential Node Connection Error for object UNDEFINED, name=BLOCK1:MEETINGROOM OA MIXING BOX
> ** ~~~ ** Node Types are still UNDEFINED -- See Branch/Node Details file for further information
> ** ~~~ ** Inlet Node : BLOCK1:MEETINGROOM OUTSIDE AIR INLET
> ** ~~~ ** Outlet Node: UNDEFINED
>


-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years


__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___