[EnergyPlus_Support] Re: HVAC Template : Zone and Plant, Should I connect the nodes ?



I'm feel so dumb, I didn't know that.

Know my simulation work correctly, I only need to adjust the parameters in view to get good results.

Thank you very much everybody.


--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Dru Crawley <dbcrawley@...> wrote:
>
> There are more than 300 example files in the
> C:\EnergyPlusV6-0-0\ExampleFiles  directory.  ExampleFiles.xls spreadsheet
> describes each of them briefly.
> 
> 
> 
> On Wed, Oct 19, 2011 at 8:14 AM, xav31sob <rockcolomiers@...> wrote:
> 
> > **
> >
> >
> > Ho, I didn't know about this file ... But I don't find it, what is the way
> > ?
> > Files--> ?
> >
> >
> > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Richard Raustad <RRaustad@>
> > wrote:
> > >
> > > Why don't you look at the example file HVACTemplate-5ZoneFanCoil.idf and
> > > see what HVACTemplate objects are used and how they are related.
> > >
> > > On 10/19/2011 6:32 AM, xav31sob wrote:
> > > >
> > > > It seem to be a problem with the Fancoil template. I don't undestand
> > > > why but the OA Mixing Box don't have any output ... I think it's my
> > > > main problem, but why ?
> > > >
> > > > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx
> > > > <mailto:EnergyPlus_Support%40yahoogroups.com>, "xav31sob"
> > > > <rockcolomiers@> wrote:
> > > > >
> > > > > The main errors :
> > > > >
> > > > > ** Warning ** Could not find Coil:Heating:Water with name
> > > > BLOCK1:MEETINGROOM HEATING COIL on any plant loop
> > > > > ** ~~~ ** Autosizing of water flow requires a heating loop
> > > > Sizing:Plant object
> > > > > ** ~~~ ** Occurs in ZoneHVAC:FourPipeFanCoil
> > > > Object=BLOCK1:MEETINGROOM FAN COIL
> > > > > ** Warning ** Could not find COIL:COOLING:WATER with name
> > > > BLOCK1:MEETINGROOM COOLING COIL on any plant loop
> > > > > ** ~~~ ** Autosizing of water flow requires a cooling loop
> > > > Sizing:Plant object
> > > > > ** ~~~ ** Occurs in ZoneHVAC:FourPipeFanCoil
> > > > Object=BLOCK1:MEETINGROOM FAN COIL
> > > > > ** Fatal ** Preceeding sizing errors cause program termination
> > > > > ...Summary of Errors that led to program termination:
> > > > > ..... Reference severe error count=2
> > > > > ..... Last severe
> > > >
> > error=FenestrationSurface:Detailed="BLOCK1:MEETINGROOM_PARTITION_5_0_0_0_0_0_WIN",
> >
> > > > invalid Building Surface Name="BLOCK1:MEETINGROOM_PARTITION_5_0_0".
> > > > > ************* Fatal error -- final processing. More error messages
> > > > may appear.
> > > > > ************* Testing Individual Branch Integrity
> > > > > ** Warning ** There are orphaned Branches in input
> > > > > ************* All Branches passed integrity testing
> > > > > ************* Testing Individual Supply Air Path Integrity
> > > > > ************* All Supply Air Paths passed integrity testing
> > > > > ************* Testing Individual Return Air Path Integrity
> > > > > ************* All Return Air Paths passed integrity testing
> > > > > ** Severe ** Node Connection Error, Node="BLOCK1:MEETINGROOM COOLING
> > > > COIL CHW INLET", Inlet node did not find an appropriate matching
> > > > "outlet" node.
> > > > > ** ~~~ ** If this is an outdoor air inlet node, it must be listed in
> > > > an OutdoorAir:Node or OutdoorAir:NodeList object.
> > > > > ** ~~~ ** Reference Object=BRANCH, Name=BLOCK1:MEETINGROOM COOLING
> > > > COIL CHW BRANCH
> > > > > ** Severe ** Node Connection Error, Node="BLOCK1:MEETINGROOM HEATING
> > > > COIL HW INLET", Inlet node did not find an appropriate matching
> > > > "outlet" node.
> > > > > ** ~~~ ** If this is an outdoor air inlet node, it must be listed in
> > > > an OutdoorAir:Node or OutdoorAir:NodeList object.
> > > > > ** ~~~ ** Reference Object=BRANCH, Name=BLOCK1:MEETINGROOM HEATING
> > > > COIL HW BRANCH
> > > > > ** Severe ** Node Connection Error, Node="BLOCK1:MEETINGROOM HEATING
> > > > COIL HW INLET", Inlet node did not find an appropriate matching
> > > > "outlet" node.
> > > > > ** ~~~ ** If this is an outdoor air inlet node, it must be listed in
> > > > an OutdoorAir:Node or OutdoorAir:NodeList object.
> > > > > ** ~~~ ** Reference Object=COIL:HEATING:WATER,
> > > > Name=BLOCK1:MEETINGROOM HEATING COIL
> > > > > ** Severe ** Node Connection Error, Node="BLOCK1:MEETINGROOM COOLING
> > > > COIL CHW INLET", Inlet node did not find an appropriate matching
> > > > "outlet" node.
> > > > > ** ~~~ ** If this is an outdoor air inlet node, it must be listed in
> > > > an OutdoorAir:Node or OutdoorAir:NodeList object.
> > > > > ** ~~~ ** Reference Object=COIL:COOLING:WATER,
> > > > Name=BLOCK1:MEETINGROOM COOLING COIL
> > > > > ** Severe ** Node Connection Error, Node="BLOCK1:MEETINGROOM MIXED
> > > > AIR OUTLET", Inlet node did not find an appropriate matching "outlet"
> > > > node.
> > > > > ** ~~~ ** If this is an outdoor air inlet node, it must be listed in
> > > > an OutdoorAir:Node or OutdoorAir:NodeList object.
> > > > > ** ~~~ ** Reference Object=FAN:CONSTANTVOLUME,
> > > > Name=BLOCK1:MEETINGROOM SUPPLY FAN
> > > > > ** Warning ** Node Connection errors shown during "fatal error"
> > > > processing may be false because not all inputs may have been retrieved.
> > > > > ** Warning ** Node Connection Error for object UNDEFINED,
> > > > name=BLOCK1:MEETINGROOM OA MIXING BOX
> > > > > ** ~~~ ** UNDEFINED not on any Branch or Parent Object
> > > > > ** ~~~ ** Inlet Node : BLOCK1:MEETINGROOM OUTSIDE AIR INLET
> > > > > ** ~~~ ** Outlet Node: UNDEFINED
> > > > > ** Warning ** Potential Node Connection Error for object UNDEFINED,
> > > > name=BLOCK1:MEETINGROOM OA MIXING BOX
> > > > > ** ~~~ ** Node Types are still UNDEFINED -- See Branch/Node Details
> > > > file for further information
> > > > > ** ~~~ ** Inlet Node : BLOCK1:MEETINGROOM OUTSIDE AIR INLET
> > > > > ** ~~~ ** Outlet Node: UNDEFINED
> > > > >
> > > >
> > > >
> > >
> > > --
> > > Richard A. Raustad
> > > Senior Research Engineer
> > > Florida Solar Energy Center
> > > University of Central Florida
> > > 1679 Clearlake Road
> > > Cocoa, FL 32922-5703
> > > Phone: (321) 638-1454
> > > Fax: (321) 638-1439 or 1010
> > > Visit our web site at: http://www.fsec.ucf.edu
> > >
> > > UCF - From Promise to Prominence: Celebrating 40 Years
> > >
> >
> >  
> >
>




------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/