Look at the system sizing results to see the impact. The OA data is input is at the zone level so it can be summed up for a system serving a number of different zones, but it isn’t included in the zone load. (Except if the OA flow rate is higher that than the design flow result based on loads). If you want OA included in the zone sizing results, use ZoneInfiltration or ZoneVentilation. From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Ery Djunaedy Folks, __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.