|
Hi, Xin
I do not have the ASHRAE document so I do know how they define the primary and secondary system. In EPlus, the two chillers on the same ChW loop is to save power. When the load is low, only one will be turned on. The PLR will be higher and more efficient. This is the large and small chiller example. Is the chiller pump the condenser pump or the water pump? The chiller has the Dx coil in the ChW tank. The ChW use side has a water circulating pump. The two pumps I mentioned below are for the two water loops. There is no water pump associated with a chiller itself. The pump is for the tank and water loop. Therefore there is no secondary pump. Two compressor pumps for two chillers. ========================== In a modular compressor system, you can have more than one mechanical pump compressor to compress the coolant into one resourviour tank, running multple Dx coils in different AHU's. (Split units) The condesor coil can be common as there is only one coolant loop. That was why I ask you to find the definition of the pri/sec system first. ================== For the COP and EIR coefficients, I think you were using the formula from another software. If the EPlus object has temperature and PLR specified, it should be a x,y equation. There are some example curves and coefficients in the DataSet directory, chillers.idf . =========== You can send me the IDF. If you use the template model, send the original IDF, not the expIDF. If you have complicated building envelop, it is better to use a 3 or 5 zone building to save time. The load size is not important in trying out the IDF. The IdealLoadsAirSystem always give you the best result. HVAC with real equipment always consumes more energy. Dr. Li To: EnergyPlus_Support@xxxxxxxxxxxxxxx From: foolishstar@xxxxxxx Date: Sat, 29 Oct 2011 20:37:53 +0800 Subject: Re:RE: [EnergyPlus_Support] multi-primary pumps+secondary pump Dear Dr. Li, I think you mis-understand my situation. I'm not trying to simulate the stand by chiller. I wonder how to simulate the chilled water pump for EACH chiller (The condenser side has no problem). I now have two chillers. Sometimes only one chiller is used and sometimes both are used. So according to the 90.1, each chiller should have a chilled water pump, right? In the last strategy, I put the pump on the chillers branch. I think it is legal because I learned it from an example called 5ZoneBranchSupplyPumps. But the error occurs. I suppose the error has to do with the secondary pump on the demand side. I don't know how to deal with it. Or it may has other solutions. In my case, both primary and secondary pumps are needed, and the primary side should have two pumps for two chillers. This is what I want to solve. PS: The primary/secondary system is a kind of chilled water system configuration. The primary pump supply water to the chiller in the supply side, and the secondary pump supply water to the end users in the demand side. It could be considered as an energy conservation measure. Thanks! Han Xing At 2011-10-29 19:50:35,"YuanLu Li" <yli006@xxxxxxxxxxx> wrote:
__._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |