Dear Forum,
I'm unable so far to figure out how to disable a DX coil in cold weather.  The AvailabilityManager:LowTemperatureTurnOFF
seems to be the right tool for the job, but it's not doing anything the way I've configured it.
The short story is this:
*  I want the Heat Pump to be available on one schedule (with fan running)
*  and its DX coil to be UNavailable when the outdoor temp <12.8C
*  I've made a separate schedule which is always "1" called "SchCpct_LowTempClgOFF" and assigned that schedule to the DX coil

Shown below is what I've done so far.  Please let me know what I am missing!  (For the record, the IO Reference and example files aren't clear to me.  They seem to say that the manager affects a schedule, not a component)

AvailabilityManagerAssignmentList
AvMgrLIST_DX_BaseSys2-11
AvailabilityManager:LowTemperatureTurnOFF
CoolingLowTempOFF_02-12-North

AvailabilityManager:LowTemperatureTurnOFF,
CoolingLowTempOFF_02-12-North,
NodeIn_OA_BaseSys2-11,
12.8,
SchCpct_LowTempClgOFF;

AirLoopHVAC:UnitaryHeatPump:AirToAir,
AirLoop_UnitCool1_BaseSys2-11,
SchCpct_FanHotelASHRAEstd, ! Note different schedule!
etc..... continuing at...
Coil:Cooling:DX:SingleSpeed,
ClgCoil_BaseSys2-11,
etc. until....
SchCpct_AlwaysOn;


Coil:Cooling:DX:SingleSpeed
ClgCoil_BaseSys2-11
SchCpct_LowTempClgOFF !  Note same schedule as used by LowTempTurnOff object
etc.



------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/