Re: [EnergyPlus_Support] Do you know the base line to create zone depth? 3.7 m or 6 m. or any





I think they are trying to specify the depth of the perimeter zones for a model using core and perimeter zoning. Per ASHRAE 90.1, this depth is 15 ft

90.1-2004 Appendix G Table G3.1 Section 8

8. Thermal Blocks ? HVAC Zones Not Designed
Where the HVAC zones and systems have not yet been designed,
thermal blocks shall be defined based on similar internal load densities,
occupancy, lighting, thermal and space temperature schedules,
and in combination with the following guidelines:
(a) Separate thermal blocks shall be assumed for interior and perimeter
spaces. Interior spaces shall be those located greater than 15 ft
from an exterior wall. Perimeter spaces shall be those located
within 15 ft of an exterior wall.
(b) Separate thermal blocks shall be assumed for spaces adjacent to
glazed exterior walls; a separate zone shall be provided for each orientation,
except that orientations that differ by less than 45 degrees
may be considered to be the same orientation. Each zone shall
include all floor area that is 15 ft or less from a glazed perimeter
wall, except that floor area within 15 ft of glazed perimeter walls
having more than one orientation shall be divided proportionately
between zones.
(c) Separate thermal blocks shall be assumed for spaces having
floors that are in contact with the ground or exposed to ambient
conditions from zones that do not share these features.
(d) Separate thermal blocks shall be assumed for spaces having
exterior ceiling or roof assemblies from zones that do not share
these features.


__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___