[EnergyPlus_Support] Re: Do you know the base line to create zone depth? 3.7 m or 6 m. or any
Thanks Jason,
It really helpful.
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Jason Kirkpatrick <jason.alan.kirkpatrick@...> wrote:
>
> I think they are trying to specify the depth of the perimeter zones for a
> model using core and perimeter zoning. Per ASHRAE 90.1, this depth is 15 ft
>
> 90.1-2004 Appendix G Table G3.1 Section 8
>
> 8. Thermal Blocks ? HVAC Zones Not Designed
> Where the HVAC zones and systems have not yet been designed,
> thermal blocks shall be defined based on similar internal load densities,
> occupancy, lighting, thermal and space temperature schedules,
> and in combination with the following guidelines:
> (a) Separate thermal blocks shall be assumed for interior and perimeter
> spaces. Interior spaces shall be those located greater than 15 ft
> from an exterior wall. Perimeter spaces shall be those located
> within 15 ft of an exterior wall.
> (b) Separate thermal blocks shall be assumed for spaces adjacent to
> glazed exterior walls; a separate zone shall be provided for each
> orientation,
> except that orientations that differ by less than 45 degrees
> may be considered to be the same orientation. Each zone shall
> include all floor area that is 15 ft or less from a glazed perimeter
> wall, except that floor area within 15 ft of glazed perimeter walls
> having more than one orientation shall be divided proportionately
> between zones.
> (c) Separate thermal blocks shall be assumed for spaces having
> floors that are in contact with the ground or exposed to ambient
> conditions from zones that do not share these features.
> (d) Separate thermal blocks shall be assumed for spaces having
> exterior ceiling or roof assemblies from zones that do not share
> these features.
>
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/